  1. #1
    Join Date
    Aug 2007
    Location
    england
    Posts
    19
    Rep Power
    0

    Daikin VRV HRV problem



    I have 5 x VKM50GBV1 HRV units with DX coils connected to a VRV 4 2 pipe system
    there are no remotes fitted and the system is wired to an I Touch
    none of the units are connected to a fan coil the HRV settings are enabled
    the mode settings have been changed for centralised control 17-7-02
    the I Touch sees the units and appears to turn them on but the units are not running
    the ventilation, freshen up and air volume have been enabled
    any ideas, thanks in advance

    The Rock
















  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin VRV HRV problem

    ook up a brc controller to check if theyve been addressed, on each unit

  3. #3
    Join Date
    Aug 2007
    Location
    england
    Posts
    19
    Rep Power
    0

    Re: Daikin VRV HRV problem

    hi install monkey

    all of the HRVs have been addressed and the I Touch can see them
    it appears that the I touch switches them on and off but when checking the HRVs are just sitting there not running

    the Rock

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin VRV HRV problem

    check each hrv unit- check for t1 t2 terminals- on the same block as the np (remote controller) and the f1f2 (transmission), also check theres power to each indoor (240v)

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin VRV HRV problem

    does the i touch show that the units are running, lil dot will show on/off/fault/timer controlled

  6. #6
    Join Date
    Aug 2007
    Location
    england
    Posts
    19
    Rep Power
    0

    Re: Daikin VRV HRV problem

    I have checked and rechecked the wiring and its all ok
    not sure what you mean by the dots but the units show up red on the I Touch
    if you mean dots like you would have to show that the filter need cleaning (timer)
    there are none showing
    If I fit remotes the units start up and run
    the I Touch is a C series the one with the pen on top
    there's power to all units and the unit count is correct on the outdoor unit

    The Rock
    Last edited by the rock; 23-05-2014 at 12:03 AM.

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Daikin VRV HRV problem

    lil dots on the bottom corner of the icons on the i touch

  8. #8
    Join Date
    Aug 2007
    Location
    england
    Posts
    19
    Rep Power
    0

    Re: Daikin VRV HRV problem

    hi install monkey

    rechecked all wiring all good and checked the I Touch there are no lil dots
    was wondering if there were any mode changes that I need to make

    The Rock

  9. #9
    Join Date
    Mar 2014
    Location
    England
    Posts
    32
    Rep Power
    0

    Re: Daikin VRV HRV problem

    Quote Originally Posted by the rock View Post
    hi install monkey

    rechecked all wiring all good and checked the I Touch there are no lil dots
    was wondering if there were any mode changes that I need to make

    The Rock
    Have you selected heat/cool master for Heat Pump