Results 1 to 11 of 11
    Apr 2012
    Iraq
    35
    623
    compressor problem with Haier mini split
    today i get a call from customer
    with this story
    he said before 2 months his Haier R22 24000 BTU mini split stopped working
    so after calling a technician
    who brought a new rotary compressor which was Toshiba ph400
    similar to the burn out one type and the replaced it
    ok
    after installing it the compressor and charging it damaged directly
    by starting drawing about 50-60 amp
    so the technician brought another compressor
    which was LG qp407
    then charged it
    he installed with these reading
    12 amp drawing
    and it cooled for about 1/2 hour then overloaded
    he called me today
    i ran the unit
    attached my manifold gauge to suction line valve
    the pressure when unit was off
    = 150 psi
    once unit started
    the pressure dropped to 0 then raised to 30 psi
    then dropped to zero
    compressor amp draw = 7 amp
    with liquid line frozen
    what is the cause
    low charge or blockage in system
    Mar 2006
    Lancashire
    1,859
    28
    Re: compressor problem with Haier mini split
    Silly question but are the new compressors exact replacements?
    Why was the first one pulling 50-60 amps? Was the voltage correct or was this low?
    If the second compressor is indeed a direct replacement and the suction pressure is dropping to 0psi and then up to 30psi then it sounds as though you have a restriction somewhere, possibly expansion device?
    Personally if it was me, then I'd look up the specs of the compressor and see what current the motor should be pulling under certain conditions and go from there.
    Marc
    Apr 2012
    Iraq
    35
    623
    yes both compressor were exact replacement
    OK about the restriction
    its possible if not the capillary tube
    it may be the indoor unit clogged
    Oct 2007
    manchester
    5,639
    45
    strainers clogged with crap or capillary if no elec exp valve, check your high side pressure.
    weigh out the gas thats in it and compare it to the name plate
    Apr 2012
    Iraq
    35
    623
    its fixed type expansion valve
    capillary tube
    ok there is no service valve on high side pressure
    just on low side
    Apr 2012
    Iraq
    35
    623
    today i opened the outdoor unit
    i found these restriction and filter
    i think of removing the restriction and the short capillary beside it and replacing the filter
    did that will decrease the efficiency or not
    Oct 2007
    manchester
    5,639
    45
    http://www.mediafire.com/view/poul6g...au28nahbea.pdf
    page 75- shows piping diagram- check valve (1 way flow) in heating mode the capillary is used
    Apr 2012
    Iraq
    35
    623
    ok
    thank u
    i cut the the cap tube end
    as marked in photo
    then i started the compressor
    the air pressure was very strong
    Oct 2007
    manchester
    5,639
    45
    below your red arrow is a strainer which goes to the liq line- cut it out and look through it
    Apr 2012
    Iraq
    35
    623
    ok
    thank u
    Apr 2012
    Iraq
    35
    623
    i cut out the filter below arrow
    it seems clean
    i removed the check valve and capillary beside it
    then i used a tube of same size of the check valve + filter
    and replaced the filter before liquid line also