    248 volt, open winding



    I have a 200v-230v 1 phase compressor that has the common winding open. Took power off, got back to it in 4 hours, same result, protector doesn't close. Checked voltage: 248 volts. Can this be the cause of the burn out?



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: 248 volt, open winding

    .

    That is about 8 - 9% over??

    I know of sites that are rated 230v and we get 252v which is near to the 10% maximum.

    It is possible, but probably unlikely.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Feb 2009
    Location
    USA
    Age
    54
    Posts
    143
    Rep Power
    16

    Re: 248 volt, open winding

    [QUOTE=Rob White;295950].

    That is about 8 - 9% over??

    I know of sites that are rated 230v and we get 252v which is near to the 10% maximum.

    It is possible, but probably unlikely.

    Rob

    I will replace it tomorrow and will cut open the old one to see what happened.