    Angry small condenser



    I have a problem
    I have purchased a unit condenser
    In order to change my unit condenser damaged in cooler milk
    I want to make sure a good choice
    I think that a very small condenser
    Information
    Ambient Temp 42
    Evaporator temperature -2
    Condensation temperature 50
    (Altitute) 0
    Refrigerant: R22
    Compressor
    When the evaporator 0 and condensing 50 = 1600 watts
    5 horse power
    TAG 4561 T. Tecumseh Europe
    R22 - Hermetic - For Medium / High Temperature Applications
    Information condenser
    GMK 25.451
    http://www.gemakltd.com/Assets/Dokum...(2012)_eng.pdf
    http://www.gemakltd.com/Assets/Dokum...R(2012)eng.pdf
    In my country there is problem the lack of cooling materials



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: small condenser

    So by the look of things your unit will provide 1.6kW @ an ambient temp of 42ºC and an evaporator temp of 0ºC.
    Is this the duty you are looking for in your milk cooler? If it is then it should work but if not then it won't work...

    Is it a good choice?
    Well here in EU anything running on R22 is a bad choice as it has been banned due to environmental issues, other than that... We just can't tell.
    It is a bit like you asking us if a Bridgestone Battlax BT 014 is a good tyre choice but not telling us anything about the vehicle it is to be fitted to apart from that it will be running on tarmac roads.

    Sorry


  3. #3
    Join Date
    Apr 2014
    Location
    Mauritania
    Age
    35
    Posts
    57
    Rep Power
    11

    Re: small condenser

    Yeah Milk Cooler
    Bro Lol This My Old Unite
    its Work But Not in Summer
    http://im62.gulfup.com/P1Z8kf.jpg

    Is it a good choice?
    bro You See The Condenser GMK 25.451 its made in turkey


    thank you To Help Me

  4. #4
    Join Date
    Apr 2014
    Location
    Mauritania
    Age
    35
    Posts
    57
    Rep Power
    11

    Arrow Re: small condenser

    Yeah Milk Cooler
    Bro Lol This My Old Unite
    its Work But Not in Summer
    http://im62.gulfup.com/P1Z8kf.jpg

    Is it a good choice?
    bro You See The Condenser GMK 25.451 its made in turkey


    thank you To Help Me

  5. #5
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: small condenser

    Why would you replace that?

    Great low rpm compressor that can be repaired using standard parts from any workshop.
    If it cuts out on HP in the summer then just replace the condenser with a larger one.

  6. #6
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: small condenser

    Maybe the motor overheats. Missing motor cowl.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  7. #7
    Join Date
    Apr 2014
    Location
    Mauritania
    Age
    35
    Posts
    57
    Rep Power
    11

    Re: small condenser

    its R12 Unite
    All R12 Now Its made by China its Rare and causes a lot of problems
    And reduces the cooling capacity its Slow

    Bro Tell Me If That Compresor Tag 4561 t And Condenser GMK 25.451 Are compatible ؟
    ٍSee
    http://im62.gulfup.com/ySkrEB.jpg
    http://im62.gulfup.com/ul53p8.jpg

  8. #8
    Join Date
    Apr 2014
    Location
    Mauritania
    Age
    35
    Posts
    57
    Rep Power
    11

    Re: small condenser

    I winding motor 6 times
    He elderly Old
    Bearings were changed 8 times
    14 years of heavy-duty
    ** Deserve of retirement

  9. #9
    Join Date
    Apr 2014
    Location
    Mauritania
    Age
    35
    Posts
    57
    Rep Power
    11

    Re: small condenser

    Quote Originally Posted by The Viking View Post
    So by the look of things your unit will provide 1.6kW @ an ambient temp of 42ºC and an evaporator temp of 0ºC.
    Is this the duty you are looking for in your milk cooler? If it is then it should work but if not then it won't work...

    Is it a good choice?
    Well here in EU anything running on R22 is a bad choice as it has been banned due to environmental issues, other than that... We just can't tell.
    It is a bit like you asking us if a Bridgestone Battlax BT 014 is a good tyre choice but not telling us anything about the vehicle it is to be fitted to apart from that it will be running on tarmac roads.

    Sorry

    bro its not 1600
    its 16000 w sorry

  10. #10
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: small condenser

    Eh? A 16 KW. I doubt that figure is right as your photo of the "Bitzer" compressor looks too small for 16 KW.
    What is the volume of milk you are chilling?
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  11. #11
    Join Date
    Apr 2014
    Location
    Mauritania
    Age
    35
    Posts
    57
    Rep Power
    11

    Arrow Re: small condenser

    Quote Originally Posted by mikeref View Post
    Eh? A 16 KW. I doubt that figure is right as your photo of the "Bitzer" compressor looks too small for 16 KW.
    What is the volume of milk you are chilling?
    bulk tank of Milk its Old System the compressor Make Ice Water And the ice water chill the milk
    Its 4400 liter Packo
    No I Say The Compressor Capacity Cooling In Temp Condenser 45c And 7c in Evaporation Its Give me 16000 Watt
    My Question
    The Compressor And The Condenser Are compatible ?
    Compresor Tag 4561 t And Condenser GMK 25.451
    ٍSee
    Refrigerant: R22
    Compressor
    When the evaporator 7 and condensing 45 = 16000 watts
    5 horse power
    TAG 4561 T. Tecumseh Europe
    R22 - Hermetic - For Medium / High Temperature Applications
    Information condenser
    GMK 25.451
    http://www.gemakltd.com/Assets/Dokum...(2012)_eng.pdf
    http://www.gemakltd.com/Assets/Dokum...R(2012)eng.pdf
    http://im62.gulfup.com/ySkrEB.jpg
    http://im62.gulfup.com/ul53p8.jpg

    In my country there is problem the lack of cooling materials

  12. #12
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: small condenser

    If your original condensing unit has produced enough ice between milking's, then we need to know the actual cooling capacity of that unit. What is the compressor model number. A Bitzer iv as in Bitzer 4? What speed does the compressor run at.
    How many litres/ gallons of milk do you chill per milking?
    Your other pictures only show a condenser and 2 compressors. Where is the rest of it?
    Last edited by mikeref; 20-05-2014 at 11:35 PM. Reason: 16 KW/ milking?
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  13. #13
    Join Date
    Apr 2014
    Location
    Mauritania
    Age
    35
    Posts
    57
    Rep Power
    11

    Re: small condenser

    Quote Originally Posted by mikeref View Post
    If your original condensing unit has produced enough ice between milking's, then we need to know the actual cooling capacity of that unit. What is the compressor model number. A Bitzer iv as in Bitzer 4? What speed does the compressor run at.
    How many litres/ gallons of milk do you chill per milking?
    Your other pictures only show a condenser and 2 compressors. Where is the rest of it?
    its bitzer open type reciprocating compressor unit number v
    its work now in min Speed Displacement 18 m3/h
    Refr R12
    in bank tank 4400 liter of Milk
    all milk come in 35c go to precooking out 12 Or 13 C And Go to the bank tank But Its Come 4 batches every hour 1000 liter

    You see in the image one Compressor The Other is liquid receiver
    its not unite Just i am I bought a compressor and condenser of the workshop to assembling

    becoz The farm need cooling quickly
    before Lost the milk
    You Know that
    moment !!

  14. #14
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: small condenser

    Working backwards,18 m3/h flow on R134a, at 40 degrees condensing, and -5 degrees SST roughly equals 6.4 KW.
    I don't have data on R12 but R134a should be close enough.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  15. #15
    Join Date
    Apr 2014
    Location
    Mauritania
    Age
    35
    Posts
    57
    Rep Power
    11

    Lightbulb Re: small condenser

    Quote Originally Posted by mikeref View Post
    Working backwards,18 m3/h flow on R134a, at 40 degrees condensing, and -5 degrees SST roughly equals 6.4 KW.
    I don't have data on R12 but R134a should be close enough.
    Yeah Its Almost but My New Compressor capacity bigger than the old

    Were assembled the unit
    I will install it tomorrow
    I am afraid of high pressure
    * Performance of the condenser!!! One fan and little an area of ​​exchange
    Fan speed 1250 t/minute
    After the unit is installed and tested
    the unit will renovate the old
    New motor and condenser New
    And examination of Pistone and the rest of the parts
    Tell me your opinion
    It's important to me ؟
    http://im74.gulfup.com/SXNR5z.jpg
    http://im74.gulfup.com/TLhuY4.jpg

  16. #16
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: small condenser

    5Hp sounds about right to me, don't know about the condenser, it looks like it should work is all i can say!
    As a rule of thumb its around 1hp per 200 gallons for ice bank tanks.
    I know Serap run their R22 stuff with around 440psi high pressure cut out for tropical environments.
    Mostly found in Oxfordshire, UK :)

  17. #17
    Join Date
    Apr 2014
    Location
    Mauritania
    Age
    35
    Posts
    57
    Rep Power
    11

    Re: small condenser

    Quote Originally Posted by monkey spanners View Post
    5Hp sounds about right to me, don't know about the condenser, it looks like it should work is all i can say!
    As a rule of thumb its around 1hp per 200 gallons for ice bank tanks.
    I know Serap run their R22 stuff with around 440psi high pressure cut out for tropical environments.
    Yes, it's 5 hp
    Thank you for rule
    In cooling milk there are a lot of problems
    In tropical areas

    But Im Us Pre Cooling The Milk Go To The Tank 11 Or 12 And 4 Time 1000 Liter Every Hour
    But Thank You

  18. #18
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: small condenser

    You are going to use R22 instead of R12 right?
    R22 runs at a much higher pressure and your new compressor will need adequate cooling to keep your discharge temperature and pressure low. You have to change the expansion valve and the orifice that feeds the ice bank to a type made for R22.
    As your ambient temperature is over 40 C, there is a chance your condenser might not be big enough to remove enough heat and you are left with a liquid/ vapour mix at a high pressure and temperature as the refrigerant leaves the condenser.
    This has several follow on effects but you can slow down the refrigerant flow with a CPR valve. (Compressor pressure Regulator.)..... "Crankcase pressure regulator" for you guys looking to correct me.
    Last edited by mikeref; 22-05-2014 at 09:06 AM.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  19. #19
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: small condenser

    Quote Originally Posted by monkey spanners View Post
    5Hp sounds about right to me, don't know about the condenser, it looks like it should work is all i can say!
    As a rule of thumb its around 1hp per 200 gallons for ice bank tanks.
    I know Serap run their R22 stuff with around 440psi high pressure cut out for tropical environments.
    Ouch!! 440 PSI on R22 converts to something higher than 65 C.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  20. #20
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: small condenser

    Op could use an EPR but that depends on the number of individual circuits running through his ice bank.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  21. #21
    Join Date
    Apr 2014
    Location
    Mauritania
    Age
    35
    Posts
    57
    Rep Power
    11

    Re: small condenser

    Quote Originally Posted by mikeref View Post
    You are going to use R22 instead of R12 right?
    R22 runs at a much higher pressure and your new compressor will need adequate cooling to keep your discharge temperature and pressure low. You have to change the expansion valve and the orifice that feeds the ice bank to a type made for R22.
    As your ambient temperature is over 40 C, there is a chance your condenser might not be big enough to remove enough heat and you are left with a liquid/ vapour mix at a high pressure and temperature as the refrigerant leaves the condenser.
    This has several follow on effects but you can slow down the refrigerant flow with a CPR valve. (Compressor pressure Regulator.)..... "Crankcase pressure regulator" for you guys looking to correct me.
    Yeah I prepare One EXV TEX2 With orifice 05
    For The New Unite
    R22 Is Much High Temperature But Small Compressor And Pipe AND More Efficacy
    Capacity Cooling Is Biger Than R12 Or 134A


    yeah Bro Its Clear
    crankcase pressure regulator limits compressor
    operation and start-up if the suction
    pressure becomes too high. But If Pressure Too Low = More Compression Work And Low High Pressur !! Its True Or Incorrect ؟ Its Help
    And EPR : to modulate the pressure in the evap based on the load and keep the evap pressures above the freezing point
    I think a im Need To instal KVR condensing pressure regulator To Separate The Vapor in Outlet Of The Condenser (Vapor In The Receiver Go To Compressor Inlet )
    correct me Bro
    I think A I'm Wrong Like Every Time !!
    But The Summer Her Just Tow Months And Some Day 34C or 36C
    Rarely Temp Go To 42C
    Time To Chill Milk Is in Mourning And Evening
    Milk Most Be Cool Before Noon

  22. #22
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: small condenser

    Specifications on your condenser show 2 possibilities so i'll go with the smaller one that's rated at 10.3 KW.
    It seems rather small for 10.3 KW but it does have significant depth.
    A CPR is mainly used on freezer rooms to limit the start up load after defrost. In your case, i was thinking it might have to be used if your suction pressure went beyond say...70 PSI (483 KPA) on start up and caused your compressor and condenser to struggle with that volume at 40 C before the TX throttles back.
    It's a different story if you have a flood back at 70 PSI.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  23. #23
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: small condenser

    Ah, suggesting a hot gas bypass tends to tell me you have an oversized compressor. (KVR?)
    Hot gas bypass is a method used to raise the suction pressure and slow liquid refrigerant flow to your ice bank.
    Hot Gas bypass also raises compressor temperature and reduces a sealed compressor's life.
    Last edited by mikeref; 23-05-2014 at 09:21 AM. Reason: Something smells off. Sniff...sniff.....just my evening meal on the gas stove turning into charcoal.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  24. #24
    Join Date
    Apr 2014
    Location
    Mauritania
    Age
    35
    Posts
    57
    Rep Power
    11

    Re: small condenser

    Quote Originally Posted by mikeref View Post
    Ah, suggesting a hot gas bypass tends to tell me you have an oversized compressor. (KVR?)
    Hot gas bypass is a method used to raise the suction pressure and slow liquid refrigerant flow to your ice bank.
    Hot Gas bypass also raises compressor temperature and reduces a sealed compressor's life.
    Yeah Ma Bro
    Now
    Finishing touches on the installation
    Charge the the ***** and will tell you the result
    Thank you for the explanation to me to support me
    God bless you