    COP cooling and heating



    Hi all,

    I'm currently using cool pack software for plotting some pressure enthalpy diagrams, this software gives me the COP of the system, I'm vaguely aware of using the chart to find the refrigeration effect, work by compressor, and total heat of rejection. Plotting on cool pack software using evp pressure cond pressure sub cool and superheat.

    Ref effect/work by comp =cop

    I want to know how to calculate the cop heating, given a certain set of inputs, It's in relation to air and ground source heat pumps, cooling isn't really important.

    Can anyone help?



  2. #2
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,876
    Rep Power
    28

    Re: COP cooling and heating

    Quote Originally Posted by jdunc2301 View Post
    Hi all,

    I'm currently using cool pack software for plotting some pressure enthalpy diagrams, this software gives me the COP of the system, I'm vaguely aware of using the chart to find the refrigeration effect, work by compressor, and total heat of rejection. Plotting on cool pack software using evp pressure cond pressure sub cool and superheat.

    Ref effect/work by comp =cop

    I want to know how to calculate the cop heating, given a certain set of inputs, It's in relation to air and ground source heat pumps, cooling isn't really important.

    Can anyone help?
    Just add 1 to your cooling COP to get COPh
    The difference between genius and stupidity is that genius has its limits.

    Marc

  3. #3
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    372
    Rep Power
    22

    Re: COP cooling and heating

    so with an example of 3.5 cop literally just add 1? so 4.5

    how accurate is that? will be using as a tool to shut problems up

  4. #4
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: COP cooling and heating

    Quote Originally Posted by jdunc2301 View Post
    so with an example of 3.5 cop literally just add 1? so 4.5

    how accurate is that? will be using as a tool to shut problems up

    It is 100% accurate.

    Think about what your Total Heat of Rejection is??

    Heat of Rejection is Refrigeration Effect (RE) and compressor Work Done (WD) added together.

    So COP of Heat output will always be one higher than COP of cooling.

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..