    Apr 2007
    30
    372
    COP cooling and heating
    Hi all,
    I'm currently using cool pack software for plotting some pressure enthalpy diagrams, this software gives me the COP of the system, I'm vaguely aware of using the chart to find the refrigeration effect, work by compressor, and total heat of rejection. Plotting on cool pack software using evp pressure cond pressure sub cool and superheat.
    Ref effect/work by comp =cop
    I want to know how to calculate the cop heating, given a certain set of inputs, It's in relation to air and ground source heat pumps, cooling isn't really important.
    Can anyone help?
    Mar 2006
    Lancashire
    1,869
    21
    Re: COP cooling and heating
    Quote Originally Posted by jdunc2301 View Post
    Hi all,
    Can anyone help?
    Just add 1 to your cooling COP to get COPh
    Marc
    Apr 2007
    30
    372
    so with an example of 3.5 cop literally just add 1? so 4.5
    how accurate is that? will be using as a tool to shut problems up
    May 2012
    1,264
    28
    It is 100% accurate.
    Think about what your Total Heat of Rejection is??
    Heat of Rejection is Refrigeration Effect (RE) and compressor Work Done (WD) added together.
    So COP of Heat output will always be one higher than COP of cooling.
    Rob