    Jul 2005
    Belarus
    pressure in the system
    Hi experts,
    I have deal with 2 multi-decks.
    They have system with capillary tube. They work good.
    I checked pressure in the system through Shrader valve on the compressor.
    The evaporating pressure of each during work is 3,3 bar.
    But when I stoped multi-decks for 48 hours and checked pressure in the system. It was different (6.0 bar and 6.4 bar). Why? The system has equal amount of refrigerant (R22) and multi-decks are staying near.
    Which factors can influence on it?
    Thanks for any advice.
    Mar 2006
    Merate (LC) - Italy
    2,549
    Re: pressure in the system
    Are you using the same gauges or are you reading the pressure with two different sets of gauges?
    11,024
    A small heat source near one system perhaps?
    Aug 2004
    744
    A little bit of air in one of them ???
    cheers
    eggs
    Jul 2005
    Belarus
    Thank you for answer.
    I'm using the same gauges for reading the pressure.
    May be sunlight is small heat source?
    I know multi-decks was charged by Galileo TP fluid refrigerant charging machine.
    Mar 2006
    Merate (LC) - Italy
    2,549
    Of course sun is a heat source, the only one around. :-)
  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Last Post: 21-03-2012, 10:09 PM
  2. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Last Post: 07-05-2010, 09:24 AM
  3. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Last Post: 23-03-2010, 12:39 PM
  4. Replies: 19