    pressure in the system



    Hi experts,
    I have deal with 2 multi-decks.
    They have system with capillary tube. They work good.
    I checked pressure in the system through Shrader valve on the compressor.
    The evaporating pressure of each during work is 3,3 bar.
    But when I stoped multi-decks for 48 hours and checked pressure in the system. It was different (6.0 bar and 6.4 bar). Why? The system has equal amount of refrigerant (R22) and multi-decks are staying near.
    Which factors can influence on it?

    Thanks for any advice.



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: pressure in the system

    Are you using the same gauges or are you reading the pressure with two different sets of gauges?

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: pressure in the system

    A small heat source near one system perhaps?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: pressure in the system

    A little bit of air in one of them ???

    cheers

    eggs

  5. #5
    Join Date
    Jul 2005
    Location
    Belarus
    Age
    51
    Posts
    25
    Rep Power
    0

    Re: pressure in the system

    Thank you for answer.

    I'm using the same gauges for reading the pressure.
    May be sunlight is small heat source?
    I know multi-decks was charged by Galileo TP fluid refrigerant charging machine.

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: pressure in the system

    Of course sun is a heat source, the only one around. :-)

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  3. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  4. Replies: 19
    Last Post: 15-04-2008, 07:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •