    cooling water TDS



    dear all
    this is my inquiry:
    what is the maximum TDS (total dessolved solids) in cooling water of the cooling tower ?
    what is the additives used in the cooling water ?
    thanks
    faithfully/ afeef



  2. #2
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: cooling water TDS

    Maximum concentration should not exceed 300 ppm and to ensure that TDS does not increase you need to have Bleed off and add fresh water with less than 150 mm water as the make up.
    Addition of chemicals to ensure the pH is slightly alkaline say pH of 7.5 to 7.8 would be better.