    SuperCritical



    Hey Guys,

    I'm having a hard time finding out the repercussions of have a refrigerant (e.g. R410a) being in the supercritical stage, for a standard AC system. At the moment, I only know that it is hard to define whether the refrigerant is a vapour or liquid form when it is supercritical. Apart from this what are some other problems?

    Thanks.



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: SuperCritical

    .

    Supercritical? Do you mean when the refrigerant is above the critical point?

    We call that transcritical.

    From what I know 410a does not react well to being transcritical (supercritical).

    Some natural refrigerants like C02 can run at transcritical temps/pressures but
    man made HFC's burn out or thermally decompose if they are exposed to the
    critical temp/pressure for prolonged periods of time and if you run HFC's at transcritical
    pressures/temps it will almost certainly "burn out".

    With transcritical pressures you don't have a change of state like you do in subcrital
    systems, the change in state only happens with a reduction of the pressure.
    So that means you don't have condensers, you have gas coolers and then a
    pressure reducing valve to create the phase change from vapour to liquid.

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Sep 2013
    Location
    Aus
    Posts
    13
    Rep Power
    0

    Re: SuperCritical

    Quote Originally Posted by Rob White View Post
    .

    Supercritical? Do you mean when the refrigerant is above the critical point?

    We call that transcritical.

    From what I know 410a does not react well to being transcritical (supercritical).

    Some natural refrigerants like C02 can run at transcritical temps/pressures but
    man made HFC's burn out or thermally decompose if they are exposed to the
    critical temp/pressure for prolonged periods of time and if you run HFC's at transcritical
    pressures/temps it will almost certainly "burn out".

    With transcritical pressures you don't have a change of state like you do in subcrital
    systems, the change in state only happens with a reduction of the pressure.
    So that means you don't have condensers, you have gas coolers and then a
    pressure reducing valve to create the phase change from vapour to liquid.

    Regards

    Rob

    .
    Hi Rob,

    Thanks for the reply, yes I meant when the refrigerant was about it's critical point.

    What do you mean about the refrigerant thermally decomposing or 'Burn Out', can you go into a bit more detail?

    Thanks.

  4. #4
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: SuperCritical

    Quote Originally Posted by the-researcher View Post
    Hi Rob,

    Thanks for the reply, yes I meant when the refrigerant was about it's critical point.

    What do you mean about the refrigerant thermally decomposing or 'Burn Out', can you go into a bit more detail?

    Thanks.
    If it runs too hot for too long it breaks down thermally,
    just the same as if you were to burn the refrigerant with
    a flame.

    Have you ever brazed a pipe with some refrigerant inside?
    the results can be quite extreme, the refrigerant burns
    and the burnt gasses react differently (they are also toxic
    and generally nasty).

    But in a sealed system those "burnt out" gasses can't go anywhere
    so you have a refrigerant that no longer works the same as the original
    refrigerant that was put in there in the first place.

    HFC refrigerants do not react too well to being run too close to the
    critical temperature and if they are ran too close to it they break down
    or "burn out"

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  5. #5
    Join Date
    Sep 2013
    Location
    Aus
    Posts
    13
    Rep Power
    0

    Re: SuperCritical

    Thanks for all the help Rob, that makes it very clear.

  6. #6
    Join Date
    Sep 2013
    Location
    Aus
    Posts
    13
    Rep Power
    0

    Re: SuperCritical

    Hi Rob,

    Just one last question on refrigerants being in transcritical stage. You stated that HFC are prone to being "burn out", how about natural refrigerants such as R290 going close to or beyond it's critical temperature and pressure, do they also "Burn Out"?

    Thanks.

  7. #7
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: SuperCritical

    Quote Originally Posted by the-researcher View Post
    Hi Rob,

    Just one last question on refrigerants being in transcritical stage. You stated that HFC are prone to being "burn out", how about natural refrigerants such as R290 going close to or beyond it's critical temperature and pressure, do they also "Burn Out"?

    Thanks.
    Natural refrigerants are less problematic and C02 is perfect for it.

    Consider using C02?

    Regards

    rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..