08-05-2014, 04:23 AM #1
Grasso Compressor fault
Hi
can some one please explain what the following fault is i am experiencing.
Intermediate pressure limiter HP compressor active
Will this effect the compressor ability as we are experiencing problems achieving temperature on a polobed full of brine. They assure me the brine strengh is correct.
The Booster compressor capacity slide value is 88% but the HP compressor only goes to 44% but the compressor is achieving a suction pressure setpoint of 0.55Last edited by Markridgway; 08-05-2014 at 04:08 PM.
-
08-05-2014, 05:58 PM #2
Re: Grasso Compressor fault
have you checked the liquid injection.also check valves and springs
-
08-05-2014, 05:59 PM #3
- Join Date
- Sep 2009
- Location
- Iran
- Age
- 66
- Posts
- 672
- Blog Entries
- 1
- Rep Power
- 19
Re: Grasso Compressor fault
could you write suction pressure and intermediate and also high pressure .
you wrote your booster compressor running with %88 and second stage compressor running with %44
what is the set point of them ?
what type of compressor you are using .
what is the temperature of them ( suction-intermediate -high).Last edited by mbc; 08-05-2014 at 06:01 PM.
-
09-05-2014, 01:48 AM #4
Re: Grasso Compressor fault
Hi
I do not know the system, but alarm would seem to indicate the inter cooler is out of spec..
Start with re calibrating pressure and temp inputs to control system.