Daikin inverter not working after cleaning of condensor coil
Hi guys , does anyone experience only outdoor fan running for a few sec than reset again without running the compressor . ( happen only after cleaning condenser coil with garden hose ) no error code from the indoor however outdoor service monitor shown *output current . Daikin outdoor model : 3MK75DVM . Any help will be greatly appreciated , I am from Singapore so we only run on cooling mode .
-
06-05-2014, 08:22 PM #2
Re: Daikin inverter not working after cleaning of condensor coil
Water or damp on electronics?
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
06-05-2014, 08:24 PM #3
Re: Daikin inverter not working after cleaning of condensor coil
as brian says damp, the outdoor fan is dc and has a pcb inside, they are prone to fail- leaving it off overnight may cure it- as with the thermo on signal the outdoor fan starts first then the inverter compressor