    I want to make chiller - I have a compressor and condenser capacity cooling 25 kw
    purchased brazed heat exchanger Swep v25THx48 / 1 b - CES
    ** I want to help in the selection of the flow of water and pump
    QOrSs-s9CEt8.jpgQOrSs-TulnMI.jpgand water inlet and outlet and other stuff
    My first post in the forum:
    I hope to help
    Sorry for the bad English...



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Some problem with SWEP brazed plate

    Plate manufacturer will provide those details.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Apr 2014
    Location
    Mauritania
    Age
    35
    Posts
    57
    Rep Power
    11

    Re: Some problem with SWEP brazed plate

    Mr Brian
    I contacted them a week ago
    But there was no answer
    However thank you anyway

  4. #4
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Some problem with SWEP brazed plate

    You have this the wrong way around, you sort all the other stuff first then select your heat ex-changer.
    SWEP do not give nominal ratings.
    So you say you have 25Kw, and what refrigerant, what is SSt and SCT and liquid temp.
    what are you chilling, from what temp to what required temp, how much of it.
    Do that then I will run through a program for you. to give you pressure drop of the heat exchanger

  5. #5
    Join Date
    Apr 2014
    Location
    Mauritania
    Age
    35
    Posts
    57
    Rep Power
    11

    Re: Some problem with SWEP brazed plate

    type of refrigerant R22
    -10°C SST/ 47°C SCT
    Water temperature 35 c
    But I want it to cool the water glycol to -2 c at night in the 3000-liter tank
    To be used in the day to precooling milk on a small dairy

    thanks to replay

  6. #6
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Some problem with SWEP brazed plate

    Quote Originally Posted by beida View Post
    type of refrigerant R22
    -10°C SST/ 47°C SCT
    Water temperature 35 c
    But I want it to cool the water glycol to -2 c at night in the 3000-liter tank
    To be used in the day to precooling milk on a small dairy

    So you have 2 tanks, a full one and an empty one.

    thanks to replay
    So you have 2 tanks, a full one and an empty one.

  7. #7
    Join Date
    Apr 2014
    Location
    Mauritania
    Age
    35
    Posts
    57
    Rep Power
    11

    Re: Some problem with SWEP brazed plate

    Yes the chiller works at night in order to cool the tank 3000 liters
    Even -2 c
    in order to used in milk precooling in the daytime

  8. #8
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Some problem with SWEP brazed plate

    Hi
    is the 35' C water the condenser water or the glycol mix start temperature you want to chill to -2.0'C.

  9. #9
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Some problem with SWEP brazed plate

    Quote Originally Posted by beida View Post
    Yes the chiller works at night in order to cool the tank 3000 liters
    Even -2 c
    in order to used in milk precooling in the daytime
    I know want you want to do, but you do not.
    I will point you in right direction.
    and the end of milk processing you have tank of water/glycol mix at ?????C. I start to refrigerate the glycol mix, do I cool from ????? (as above) to -2C in one go, or do I chill the glycol mix from ????? to a slighlty colder temp, so that over night the whole tank is a -2C.
    So describe what you want the refrigeration to do, and not only the final out come.

  10. #10
    Join Date
    Apr 2014
    Location
    Mauritania
    Age
    35
    Posts
    57
    Rep Power
    11

    Re: Some problem with SWEP brazed plate

    yeah right direction. This is what I want
    in the end of milk processing Often the temperature of the water/glycol mix 16 C or 18 C
    There are 12 hours before the second milk processing
    all night to cool the 3000 liter to -2 C From 18C or 20C
    Thank you for caring ^__^

  11. #11
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Some problem with SWEP brazed plate

    what is the model number of the compressor
    and how much milk are you cooling per day

  12. #12
    Join Date
    Apr 2014
    Location
    Mauritania
    Age
    35
    Posts
    57
    Rep Power
    11

    Re: Some problem with SWEP brazed plate

    compressor BRISTOL H2BG104DBEE
    The amount of milk in 2800 and almost a liter
    Receiving sporadic 400 liters of milk every half hour
    We are in the center of the dairy farms of rural

  13. #13
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Some problem with SWEP brazed plate

    Using a 25% polypropylene glycol mixture you a flow of 1.1Kgs/second, 31Kpa pressure drop (plus pipework)
    This will give peak duty of around 30Kw (at the start), and drop down to around 10Kw at the end.
    Do not have full detail on Bristol compressors, but should be close enough and keep the comp with in envelope.
    With such a varing load I would look at an electronic expansion valve.

  14. #14
    Join Date
    Apr 2014
    Location
    Mauritania
    Age
    35
    Posts
    57
    Rep Power
    11

    Re: Some problem with SWEP brazed plate

    Thank you, my brother
    In my electronic expansion valve is not available
    Just Danfoss expansion valve Thermo
    about the bristol
    http://mail4.ansal.com.ar/Documentacion/pdfs/197803.pdf

  15. #15
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Some problem with SWEP brazed plate

    Quote Originally Posted by beida View Post
    Thank you, my brother
    In my electronic expansion valve is not available
    Just Danfoss expansion valve Thermo
    about the bristol
    http://mail4.ansal.com.ar/Documentacion/pdfs/197803.pdf
    The numbers were close enough, i had the displacement.
    Size you danfoss for 20Kw 0SST and 48CSCT, that should cover the application range.

  16. #16
    Join Date
    Apr 2014
    Location
    Mauritania
    Age
    35
    Posts
    57
    Rep Power
    11

    Re: Some problem with SWEP brazed plate

    Thank my teacher
    Mission Accomplished
    What do you recommend in order to learn cooling?
    Lift my hat out of respect to you

  17. #17
    Join Date
    Apr 2014
    Location
    Mauritania
    Age
    35
    Posts
    57
    Rep Power
    11

    Re: Some problem with SWEP brazed plate

    Hi Bro ^_^
    There have in my store Some water pump
    is the best types in my country
    I have two pump
    Cp 130 And Cp 132A

    http://i57.tinypic.com/98vdd4.png

  18. #18
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Some problem with SWEP brazed plate

    It is not water, so is harder to pump
    so go for CP150 and install a gate valve on the discharge to control flow rate

  19. #19
    Join Date
    Apr 2014
    Location
    Mauritania
    Age
    35
    Posts
    57
    Rep Power
    11

    Re: Some problem with SWEP brazed plate

    thnks my Bro

  20. #20
    Join Date
    Apr 2014
    Location
    Mauritania
    Age
    35
    Posts
    57
    Rep Power
    11

    Re: Some problem with SWEP brazed plate

    Tell me why Mix glycol by 30% to get the water temperature -2c. *
    Is it related the evaporation temperature of R22 -10c if water -2c ?
    They say to get the water temperature -2c Mix 16% propylene glycol?