Results 1 to 5 of 5
  1. #1
    Join Date
    May 2014
    Location
    florida
    Age
    75
    Posts
    2
    Rep Power
    0

    pumping down to the evap



    I have pumped systems down to the condenser side before but not the evap side. Could someone post the steps to pump down a carrier split system so I can replace the accumulator. I know it is done in the heat mode and probably is done just as to the condenser side but just in the reverse. Any things I should be aware of. I'm sure you won't get all the refrigerent out past the service valves this way.



  2. #2
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: pumping down to the evap

    heat mode close the liq/small line valve. job done assuming the indoor unit can hold the charge.

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: pumping down to the evap

    Think I'd recover the whole charge, would be able to change the filter drier then as well (assuming its in the line set). Plus you won't have any worries of the valves letting by as you are brazing the new accumulator in.
    Mostly found in Oxfordshire, UK :)

  4. #4
    Join Date
    May 2014
    Location
    florida
    Age
    75
    Posts
    2
    Rep Power
    0

    Re: pumping down to the evap

    Thanks for the responses.

  5. #5
    Join Date
    Sep 2008
    Location
    england
    Posts
    427
    Rep Power
    20

    Re: pumping down to the evap

    Tkae the whole charge out, it won`t take much longer (getting all the other gear ready in the meantime) and you`ll have the benefit of knowing if the correct charge was still in there when you weigh it out.