    Question Is there a way to work out operating pressure?



    Hey everyone, new to the forums. I was just wondering if there's a standard way to work out operating pressures. Basically I'm asking if there is a formula to follow to work out operating pressures on different forms of refrigeration. Thanks in advance



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Is there a way to work out operating pressure?

    .

    Refrigerant pressures are directly affected by refrigerant temp.

    You need to understand the basic principles of a refrigeration system
    and then that information would be used to tell you the pressures.

    Its all to do with temperature / Pressure relationships of the refrigerant.

    Different refrigerants work at different pressures which is why some refrigerants
    are better at low temperature or some refrigerants are better at high temperature
    than others.

    The first thing to know is that in most (vapour compression) systems the refrigerant is
    in one of two states.

    It is either in liquid form or it is in vapour (gas) form and your gauges only shows
    the point where the refrigerant changes from a vapour to a liquid or from a liquid to a vapour.

    In the system we absorb and reject heat and the places where that is done is inside
    the evaporator and condenser.

    In the evaporator we "evaporate" the liquid and change it to a vapour.
    In the condenser we "condense" the vapour and change it to a liquid.

    Your gauges show the pressure and the temperature that, that happens at.

    https://www.google.co.uk/search?q=pr...sm=93&ie=UTF-8

    http://www.agas.com/upload/product/0...33235_1074.pdf

    Regards

    Rob

    .
    Last edited by Rob White; 30-04-2014 at 09:04 AM.
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Is there a way to work out operating pressure?

    Basically:

    You reject heat at the condenser. For a change of state refrigerant, that means its saturation temperature needs to be higher that the temperature of your cooling medium. If your cooling medium is air and weather data says that 1% of a year you will hit 35-deg. C ambient, the refrigerant in the condenser will need to be somewhat warmer than that. Buy a whole bunch of condenser, and you might get it to work at 38 Deg C....For more practical circuits something like 43 to 47 Deg C would be expected. Of course if you can reject that heat to well water at 25 Deg C. you can operate at a lower condensing temperature. And whatever that temperature is, there is a corresponding saturation pressure, presuming a singular pure fluid.

    The opposite prevails on the evaporating side: for the refrigerant to absorb heat from whatever it is you are trying to cool, the refrigerant needs to be at a lower temperature than the cooled medium. There's a lot more considerations and variations dealing with the evaporating side, but if you are trying to make a 0-deg. C space, you will need to "suck" hard enough to maintain the refrigerant at least a few degrees colder. With that lower temperature corresponds a saturation pressure.....

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Is there a way to work out operating pressure?

    At start of this forum section you have sticky thread named Refrigeration 101. Try to read that whole thread before next question.
    http://www.refrigeration-engineer.co...rigeration-101

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Is there a way to work out operating pressure?

    Formula is:
    te=wet bulb temperature of air at evaporator inlet - TD of evaporator => convert that in to saturation pressure of used refrigerant
    tc=dry bulb temperature of air + TD condenser =>convert that in to saturation pressure of used refrigerant