    freezer low suction pressure



    Hi I have a copeland scroll condensing unit running a freezer coldroom, the unit gets down to -21c in no time and sight glass full with the occasional bubble . The only worry I have is the suction pressure is about 4-6psi which to me is too low. Liquid pressure is 200psi it has a new drier exp valve and orifice. So no blockages. Any info would be great
    Alex



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: freezer low suction pressure

    Without knowing the refrigerant and suction pipe temperature we won't be able to comment

  3. #3
    Join Date
    Apr 2009
    Location
    oldham
    Age
    36
    Posts
    6
    Rep Power
    0

    Re: freezer low suction pressure

    Sorry frank its on 404a I haven't taken a suction pipe temp

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: freezer low suction pressure

    I've been working on a CO2 tank cooler today on 404a with a suction pressure of 5psig and a discharge pressure of 200 psig when I got there

    Got the discharge pressure down to 105psig by deep cleaning the condenser then found that it was quite short of gas as the pipe temp was +7C.....didn't help that there was hardly any lagging on the pipe ...oh ...and discovered that it had an R22 TEV

    Can you post a full set of system readings?

  5. #5
    Join Date
    Oct 2013
    Location
    England
    Age
    36
    Posts
    147
    Rep Power
    14

    Re: freezer low suction pressure

    Quote Originally Posted by frank View Post
    I've been working on a CO2 tank cooler today on 404a with a suction pressure of 5psig and a discharge pressure of 200 psig when I got there

    Got the discharge pressure down to 105psig by deep cleaning the condenser then found that it was quite short of gas as the pipe temp was +7C.....didn't help that there was hardly any lagging on the pipe ...oh ...and discovered that it had an R22 TEV

    Can you post a full set of system readings?
    You weren't at a nationwide bank in reading were you?

  6. #6
    Join Date
    Apr 2009
    Location
    oldham
    Age
    36
    Posts
    6
    Rep Power
    0

    Re: freezer low suction pressure

    Condensing unit about6 month old was on r22

  7. #7
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: freezer low suction pressure

    Check the txv,put a 404a valve on if it has not got one already and check bulb contact on outlet.

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: freezer low suction pressure

    Quote Originally Posted by NewmanRef View Post
    You weren't at a nationwide bank in reading were you?
    Do they have a 12tonne CO2 tank as well?

  9. #9
    Join Date
    Apr 2009
    Location
    oldham
    Age
    36
    Posts
    6
    Rep Power
    0

    Re: freezer low suction pressure

    The valve is 404a and I checked the bulb which was sat on top of tue pipe so I moved it to the side which helped a little. Im gonna change the valve tomorrow and see if that helps. Cheers frank

  10. #10
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: freezer low suction pressure

    Has it got the correct orifice in it? It would needed a bigger one than it had on R22.
    Mostly found in Oxfordshire, UK :)