Nite shades causing frozen product
I was always under the impresion that temperature follows pressure period. So if a cut out pressure setting produces a 20 degree coil temperature, which produces a 30 degree discharge air temp, which in turn gets you a 40 degree box temp ( all approximates) and nothing could change that. However, pulling down a nite shade closing an open self select merchandiser seems to produce lower case temperatures than when it is open and sometimes even freezes the product.
Could someone explain this. Thanks, Ken
-
25-03-2006, 02:46 AM #2
Re: Nite shades causing frozen product
Hi Ken,
The big difference is the amount of ambient air that gets drawn into the boxes when the covers are removed during the daytime.
When the covers are pulled down for the after business hour periods a greatly reduced volume of ambient air is allowed to be entrained into the refrigerated air.
The lower temperatures at night are due to the decreased heat loads the refrigeration system is exposed to. Therefore the system actually has extra capacity.
This is why they can freeze, when it is normally just cold.
-
25-03-2006, 03:30 AM #3
Re: Nite shades causing frozen product
I was always under the impresion that temperature follows pressure period. So if a cut out pressure setting produces a 20 degree coil temperature, which produces a 30 degree discharge air temp, which in turn gets you a 40 degree box temp ( all approximates) and nothing could change that. However, pulling down a nite shade closing an open self select merchandiser seems to produce lower case temperatures than when it is open and sometimes even freezes the product.
I am okay with everything you said until the following:
However, pulling down a nite shade closing an open self select merchandiser seems to produce lower case temperatures than when it is open and sometimes even freezes the product.
You need to control temperature with a thermostat. Air temperature has no direct relationship with evaporator temperature. That's the short answer. But permit me to throw the question back at you.
The only constant is the low pressure control cut out setting which produces a 20 deg F coil. What have you changed when you introduce covers? You have turned an open display case into a reach in. Is it unreasonable to expect the air temperature to approach closer to the evaporator temperature?
-
25-03-2006, 05:46 AM #4
Re: Nite shades causing frozen product
Ok, so reducing the load is the reason the air temperature can approach closer to the evaporator temperature. Which stated another way would mean the TD of the evaporator (entering air temp vs. leaving air temp) will generally be greater with a higher load than with a smaller load.
So the 20 degree coil (I presented as an example) now produces a 25 degree dicharge air temp , instead of 30. Which produces a lower temperature in the product.
Does that sound right?
KenLast edited by kengineering; 25-03-2006 at 05:48 AM. Reason: additional comments
-
25-03-2006, 05:20 PM #5
Re: Nite shades causing frozen product
Exactly right. The actual temperatures might be different than those you used as an example but the same logic applies.
The night covers are used to reduce the heat load on the display cases. By doing this the system run time is reduced at night.
I like Dan's response about using a thermostat. The air temperature is what you are trying to control, not the suction pressure.
If you control by suction pressure, the setting has to be adjusted for different operating conditions. When the night covers are pulled down you change the operating conditions of the display case.
-
25-03-2006, 06:00 PM #6
Re: Nite shades causing frozen product
So,is there a way to control the 2 temperatures? night temp with not alot of external factors compared to day temp. with shades up and all? the only way i can think is have someone physically adjust the stat for night or use maybe a timer or computer program as in buildings for comfort cooling,but then again what effect would it have on the product? Just thinking aloud guys,what you all think
-
25-03-2006, 06:05 PM #7
Re: Nite shades causing frozen product
When the night covers are down, less ambient air enters the display case. As the case starts to cool down, the discharge air temperature off of the evaporator decreases. The thermostat shuts off the system.
When the covers are up, more ambient air enters the case and the system runs more of the time.
No need for two thermostats. One will work just fine.
-
25-03-2006, 06:07 PM #8
Re: Nite shades causing frozen product
Many controllers in supermarket applications ((Radford, Danfoss, Eliwell, Dixell, Carel...) are having a special digital input for that so that a second higher setpoint can be chosen automatically when the curtains are closed.
Sometimes a light sensor detects the closing of the shop - shutting down the lights - closes the curtain and increases the temperature.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
26-03-2006, 03:23 AM #9
Re: Nite shades causing frozen product
Sometimes a light sensor detects the closing of the shop - shutting down the lights - closes the curtain and increases the temperature.
-
26-03-2006, 03:27 AM #10
Re: Nite shades causing frozen product
So the 20 degree coil (I presented as an example) now produces a 25 degree dicharge air temp , instead of 30. Which produces a lower temperature in the product.
Does that sound right?
Ken
-
26-03-2006, 12:21 PM #11
Re: Nite shades causing frozen product
Dan,
The light switch: there are/were different systems.
Packo made long time ago a unit that was installed on the top of a counter and this device measured the lux of the store via an LDR.
If that went under a preset value - light out in the store - then some relays were activated to shut down the lights in the cabinets, closed the curtain and switched to a second thermosta with a higher setting.
We made this device ourselve in a small switch-cupboard.
The controllers used these days for supermarkets like Danfoss, RMS/Radford, Eliwell, Dixell, Carel.... all have a second build-in second setpoint, activated via a digital input.
Many of the standard controllers (Carel, Eliwell, Dixell, and CArel) have this feature as a standard.
You can trigger this input with an LDR, or an auxillary contact of the curtain and/or the cabinet lights.
So as soon light swiches out or curtain closes, the second setpoint is activated.
You then can increase or decrease temperature relative to the setpoint (a certain DT of the setpoint) or give in an absolute value.
Some devices (Eliwell and Dixell for sure) even can regulate the temperature according to the mathematical average temperature of the air-on and the air-off temperature.
This to avoid freezing during the night.
For a counter, we increase temperature +/- 4 K higher.
For a freezer we decrease temperature 5K so that we can use the benefits of the lower electricity costs and lower ambient temperatures of the night.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
26-03-2006, 06:57 PM #12
Re: Nite shades causing frozen product
After thinking about the use of two set points I am beginning to think this is a very smart thing to do. The resetting of the night time temperature could reduce the potential for partial freezing of the food at night (on coolers).
-
26-03-2006, 09:16 PM #13
Re: Nite shades causing frozen product
Peter, is it possible, for the counters, that the temperature you are referring to is the evaporator temperature? I don't see why you would choose to warm up the discharge air temperature.
How you handle freezers intrigues me. In this case, are you actually permitting the air and product to get colder, sort of like a banking or fly-wheel system?
-
26-03-2006, 09:17 PM #14
Re: Nite shades causing frozen product
Eliwell parameter H11 and E00 till E03
An IR33 from Carel has a very intelligent self learning defrost algorithm. It can learn from the previous defrost to optimize the next one.
This device is one with the most sophisticated software available and +/- same price of an Eliwell, so cheap.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
01-04-2006, 11:16 PM #15
Re: Nite shades causing frozen product
Electrolux used a temp controler with an air on and air off the evap probes. Which calculated the product temp which you could set the air on/air off %. for use with night blinds.Worked well apart from the probes failing after time causing drift.
-
02-04-2006, 01:17 PM #16
Re: Nite shades causing frozen product
Originally Posted by Dan
For the counters, it's done for Carrefour even with controllers with 1 probe. The settemperature is raised some degrees. Evaporator temperature remains the same because they're mainly connected to a pack which keeps a stable suction temperature all the time.
We have a pack running on cold rooms (-2°C) and meat cutting rooms (10°C) The setpoint of the pack is increased when no cold rooms are asking for cold so that we can increase COP. There's also a 3th higher setpoint for night operation.
The freezers..well we store latent energy in the products and in the larger freezer rooms with a concrete floor, a lot of energy can be stored also in the floor.
A client of us with a big storage freezer room (+/- 15 x 15 x 10 m) runs his freezer (full of vegetables) from Friday evening till Monday morning at a strongly reduced electricty rate. He pulls it to -30°C and it slowly rises to -20°C till the Friday.
Test this once with your domestic freezer at home..run it the whole night in the 'Super' position and then switch it off in the morning. It will take hours before the thermostat will swich on the compressor.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
02-04-2006, 07:58 PM #17
Re: Nite shades causing frozen product
Originally Posted by Peter_1
But I know what you mean. Thermal storage using mass of the product and the floors.
Kind Regards. Andy
-
02-04-2006, 09:56 PM #18
Re: Nite shades causing frozen product
You're completely right Andy, we passed of course the latent phase of teh floro and the products.
But If you count what the mass is of the concrete floor, then you have a huge storage medium.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
02-04-2006, 11:55 PM #19
Re: Nite shades causing frozen product
In a dormant or hidden stage
We use floating suction setpoints with a target temperatuer of the most demanding refrigerator... ice cream and meat, for example. Nothing warms up, but we take advantage of letting the suction pressure rise. Using refrigeration inertia is an intriguing concept. It is almost the opposite to floating the suction pressure. Interesting.Last edited by Dan; 03-04-2006 at 12:03 AM.
-
03-04-2006, 12:20 AM #20
Re: Nite shades causing frozen product
Hi guys,
The load shifting ability you are discussing is based on the thermal capacitance of the building and/or product being stored.
The more product in storage you have provides a higher thermal capacitance.
Think of it like this: Mass X Specific Heat
This provides a certain amount of stored energy at a specific temperature. After some heat is absorbed by the product, the temperature will change.
With cold storage facilities the very large volume of stored product allows the temperature rise to be minimized during the daytime with the refrigeration system OFF, or at some reduced capacity.
The added mass of the concrete also helps.
In a true load shifting strategy, the room is over cooled during the night (lower wet and dry bulb temperatures and possibly less expensive electricity).
During the daytime (when the wet and dry bulb temperatures are higher and the electricity is more expensive) the refrigeration system is idled to minimize energy and demand charges.
-
10-04-2006, 06:39 PM #21
Re: Nite shades causing frozen product
I would like to install these on my merchandisers/coolers and I am having the worst time locating a manufacturer of these night curtains/blinds. Can anyone refer me?
-
10-04-2006, 07:10 PM #22
Re: Nite shades causing frozen product
Did this poster PM'ed you also with same message?
And this for his 1st post. You know what I think about this.
I learn my kids that they first have to introduce themselves. Am I old-fashioned?It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
10-04-2006, 07:20 PM #23
Re: Nite shades causing frozen product
I received the same message Peter.
It seems our friend must have sent this to a lot of people posting in this thread.
-
10-04-2006, 07:31 PM #24
Re: Nite shades causing frozen product
Apologies for leaving out the introduction. My name is Jessica and I am a marketing manager for Aux Svcs at a community college in Michigan. I am not an engineer- so I didn't really intend to post often enough to be introduced. I was just desperately looking for some help/guideance on something that you folks may know more about so that is why I contacted several people in the same thread seeking the same information. But again, I didn't realize that there was specific protocol for such formal introductions in this forum- I did not mean to offend. Thank you.
-
10-04-2006, 07:44 PM #25
Re: Nite shades causing frozen product
Originally Posted by Dan
Regards Victor
-
10-04-2006, 08:09 PM #26
Re: Nite shades causing frozen product
Jessica,
No problem, it's just we had some troubles the last weeks and we want to keep some etiquette on this forum.
We're almost with 5000 members worldwide and there need to be some rules.
As you already perhaps have noticed, this is a very helpfull forum with posters from China to the US, Russia, Japan Belgium, the UK....
So your question: I can give you immediately 3 addresses in Belgium but you can't do anything with this.
Have a few days patience and posters from the US will see your question and I'm sure they will give you an answer.
HELLLLOOOOO, someone can help this friendly lady?It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
10-04-2006, 08:24 PM #27
Re: Nite shades causing frozen product
Peter, some information has already been sent to her via PM.
-
11-04-2006, 12:59 AM #28
Re: Nite shades causing frozen product
Yes, all I had to do was a search for "night covers for refrigerated display cases" and I found pages of results. I also recommended Economax and Chase doors, specifically, just in case my search results did not work.
I would have responded the same had I read her question here. But all I did was a search for what Jessica was asking and there were pages of results, so I am puzzled why it was so difficult finding manufacturers. Anyway, no offense taken Jessica.