    Carrier xarios 500



    Got a box running as a freezer on standby only, road compressor blanked off.
    When on defrost suction pressure is 2.6 bar but intermittently it rises to 8 bar and cuts out on hp2 switch
    Any ideas what could cause this ?



  2. #2
    Join Date
    Nov 2009
    Location
    Canada
    Posts
    123
    Rep Power
    15

    Re: Carrier xarios 500

    Quote Originally Posted by TransCool View Post
    Got a box running as a freezer on standby only, road compressor blanked off.
    When on defrost suction pressure is 2.6 bar but intermittently it rises to 8 bar and cuts out on hp2 switch
    Any ideas what could cause this ?

    is the condenser fan running and at the right speed?

  3. #3
    Join Date
    Aug 2011
    Location
    Canada
    Posts
    160
    Rep Power
    15

    Re: Carrier xarios 500

    Quote Originally Posted by TransCool View Post
    Got a box running as a freezer on standby only, road compressor blanked off.
    When on defrost suction pressure is 2.6 bar but intermittently it rises to 8 bar and cuts out on hp2 switch
    Any ideas what could cause this ?

    What's your discharge pressure running?
    2.6 bar is the cpr setting. If the xarios 500 is the same as the NA 50x there is a bypass circuit around the CPR. When the discharge pressure rises above 27.5 bar HP4 will close, closing the bypass circuit and brings the CPR back into the system and should lower the discharge pressure as well as the suction.
    HP2 switch should cycle the fans on and open the condenser inlet solenoid at about 22 bar at 30 bar HP3 will trip and shut the unit down.

    Is the charge weight correct?

  4. #4
    Join Date
    Apr 2005
    Location
    Scotland
    Posts
    11
    Rep Power
    0

    Re: Carrier xarios 500

    Condenser fan runs and cycles on pressure switch, new motor fitted 2 months ago .there is no by pass valve near CPR only a liquid injection valve
    On defrost when operating correctly head pressure sits around 11bar and suction 2.6 bar, when fault occurs head pressure rises to approx 21 bar and suction climbs quickly to 8 bar and above, unit trips pressure switch dropping pressure does this 2 or 3 times during defrost until it terminates defrost on temp and not time
    Fitted new standby compressor last week ,changed drier vacc end out overnight and new charge of gas weighed in,unit cools fine

  5. #5
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: Carrier xarios 500

    Why did you change compressor,maybe some **** gone into system,time to strip down upstream from compressor delivery

  6. #6
    Join Date
    Apr 2005
    Location
    Scotland
    Posts
    11
    Rep Power
    0

    Re: Carrier xarios 500

    Quote Originally Posted by cadwaladr View Post
    Why did you change compressor,maybe some **** gone into system,time to strip down upstream from compressor delivery
    Unit was tripping mains supply , dead short inside compressor, drained oil on old unit and oil was clean
    If condenser solenoid valve was leaking could gas come back through oil separator and into compressor via oil return line from separator ?

  7. #7
    Join Date
    May 2011
    Location
    Romania
    Age
    40
    Posts
    84
    Rep Power
    13

    Re: Carrier xarios 500

    Condenser valve leaking will not trip any switches only low heating capacity, hot gas valve leaking would be a problem, oil separators usually will fill up with dirt and not let oil back to compressor it's a must change when road comp fails, never heard of one letting hp back into suction... If used only on stby i would remove injection valve from circuit. Do you have 8 bar on suction after stopping or during operation?

  8. #8
    Join Date
    Apr 2005
    Location
    Scotland
    Posts
    11
    Rep Power
    0

    Re: Carrier xarios 500

    Quote Originally Posted by sonkax View Post
    Condenser valve leaking will not trip any switches only low heating capacity, hot gas valve leaking would be a problem, oil separators usually will fill up with dirt and not let oil back to compressor it's a must change when road comp fails, never heard of one letting hp back into suction... If used only on stby i would remove injection valve from circuit. Do you have 8 bar on suction after stopping or during operation?
    Suction pressure only rises to 8 bar and above on defrost builds up slowly then after about 6 bar rises quickly
    Going to attend today and fit solenoid valve repair kit , will keep you guys posted
    Thanks for all the help

  9. #9
    Join Date
    May 2011
    Location
    Romania
    Age
    40
    Posts
    84
    Rep Power
    13

    Re: Carrier xarios 500

    More likely it's the CPR. Put unit on heat and try changing the cpr settings, measure vap inlet and outlet press , see if messing with the cpr changes anything on suction side.

  10. #10
    Join Date
    Apr 2005
    Location
    Scotland
    Posts
    11
    Rep Power
    0

    Re: Carrier xarios 500

    Fitted new CPR and repair kits to solenoid valves,Unit has been fine for a week now and all ok
    Thanks for all the help