    Aermec NSB Remote on/off with external volt-free contact not working



    Hello
    We have about 15 Large Aermec NSB chillers on site and all of a sudden one will not switch off via the BMS digital input nothing seems linked out or overridden and the BMS relay operates.

    any help please I'm stumped

    Mark



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Aermec NSB Remote on/off with external volt-free contact not working

    check the relay for remote on/off doesnt have continuity when its powered down, maybe swap boards with another chiller to see if the fault moves

  3. #3
    Join Date
    Feb 2008
    Location
    Surrey
    Age
    67
    Posts
    17
    Rep Power
    0

    Re: Aermec NSB Remote on/off with external volt-free contact not working

    I've checked the relay thanks and even taken the wires out of the input into the chiller PLC, it still runs and can only be stopped and started via the front panel. The only trouble is the default passwords have been changed recently by the last company that lost the contract and nobody appears to know them now, very strange.
    It think the settings have been changed so its not looking for that input anymore. The manufactures password would get me out of trouble I expect.
    Thanks Mark

  4. #4
    Join Date
    Feb 2008
    Location
    Surrey
    Age
    67
    Posts
    17
    Rep Power
    0

    Re: Aermec NSB Remote on/off with external volt-free contact not working

    It's fixed a password was found, control by digital input was switched off.