    MHI split popping fuse



    Hello,

    Got a split that was dead when I got to do the maintenance on it.
    Fuse spur had power in but the 13amp fuse had gone.

    Replaced the fuse ran up n pot tried to kick in then popped the fuse in the spur again.
    Checked the pot with my multi meter n seems ok.
    The klixon looked charred n melted a bit, had continuity on both pins.

    Reckon I need to borrow that Megger again?
    Any thoughts?

    Also my sniffer picked up a leak n traces of oil on the flares

    Cheers



  2. #2
    Join Date
    Jan 2014
    Location
    Uk
    Age
    39
    Posts
    91
    Rep Power
    12

    Re: MHI split popping fuse

    image.jpg

    Here's the klixon

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: MHI split popping fuse

    cut a peice of 1/4 pipe about 25mm long- good for 60amp! haha. siezed pot, looks like its been getting hot, prob due to lack of cooling as you say u found oil on flares

  4. #4
    Join Date
    Jan 2014
    Location
    Uk
    Age
    39
    Posts
    91
    Rep Power
    12

    Re: MHI split popping fuse

    Haha.
    So if I use the Megger, will it show it's seized? Or only show Locked rotor with a clamp?

    Cheers

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: MHI split popping fuse

    megger will only show the winding insulation is good, a clamp meter will show locked rotor when you try to run it

  6. #6
    Join Date
    Dec 2007
    Location
    uk
    Posts
    73
    Rep Power
    17

    Re: MHI split popping fuse

    Has it got a capacitor on it?

  7. #7
    Join Date
    Jan 2014
    Location
    Uk
    Age
    39
    Posts
    91
    Rep Power
    12

    Re: MHI split popping fuse

    Think so yeah

  8. #8
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    372
    Rep Power
    22
    Check uf value on capacitor... Make sure it's still good. Megger will check condition of windings. Check starting current using clamp on start up... You'll probably hear it being seized

  9. #9
    Join Date
    Jan 2014
    Location
    Uk
    Age
    39
    Posts
    91
    Rep Power
    12

    Re: MHI split popping fuse

    Came back this morning, put another fuse in, turned it on ran round to the cond n it's already popped! Could do with a hand

  10. #10
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,045
    Rep Power
    35

    Re: MHI split popping fuse

    Is there an outdoor isolator and an indoor power supply to make things easy, otherwise I'm free end of the week. :-)

    Check winding resistances and megger, check cap value on meter + charge with a megger if you fancy and check voltage to see it holds a charge and isn't shorting internally at higher voltage, check wires to comp not rubbed through and wired up right, disconnect comp and run system.

    If it runs fine then comp has gone to the great fridge God Carpigiani. RIP lil' fella.

    If fuse blows then Carpigiani has given her his blessing for continued operation so look for a dodgy fan motor, reversing valve or interconnect.
    If you have a PSC compressor I guess there is only a simple PCB if at all on the unit?

    Cheers,
    Andy.
    Health and safety first..........unless I'm in a hurry.

  11. #11
    Join Date
    Jan 2014
    Location
    Uk
    Age
    39
    Posts
    91
    Rep Power
    12

    Re: MHI split popping fuse

    I put it down to a seized pot, no isolator it's on a flex with a plug
    Spoke to an old colleague who has already wrote the pot off, turns out it's cheaper for a new system than a new pot!
    Apparently he has already put a quote in n the customer has previously said no as there is another unit in there.....

  12. #12
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: MHI split popping fuse

    you never offered to diagnose that fujitsu general!- u man whore!

    Quote Originally Posted by Tayters View Post
    Is there an outdoor isolator and an indoor power supply to make things easy, otherwise I'm free end of the week. :-)

    Check winding resistances and megger, check cap value on meter + charge with a megger if you fancy and check voltage to see it holds a charge and isn't shorting internally at higher voltage, check wires to comp not rubbed through and wired up right, disconnect comp and run system.

    If it runs fine then comp has gone to the great fridge God Carpigiani. RIP lil' fella.

    If fuse blows then Carpigiani has given her his blessing for continued operation so look for a dodgy fan motor, reversing valve or interconnect.
    If you have a PSC compressor I guess there is only a simple PCB if at all on the unit?

    Cheers,
    Andy.