    High Pressure on relief valve



    Hello and good Easter to everyone!

    I recently built a refrigeration unit with 3x10hp compressors which supports 6 chambers (@ -18 degrees celsius) with one evaporator each. All the chambers are supplied in parallel from the unit and each one of them is controlled by a thermostat and a solenoid valve. My problem is that every time a solenoid valve opens (which means a chamber started working), there is alot of tube vibration which results to tube leakages. For the supply line (of the evaporators) i used 18mm copper tube (that's the failing tube). Do you have any ideas on how to avoid that vibration?



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: High Pressure on relief valve


  3. #3
    Join Date
    Sep 2012
    Location
    greece
    Age
    32
    Posts
    5
    Rep Power
    0

    Re: High Pressure on relief valve

    Quote Originally Posted by install monkey View Post
    thank you for the quick response!

    To be honest, i dont think this will solve the problem because the vibration doesn't come from the compressor but from the liquid inside the tube, when the solenoid valve is open and the liquid hits the relief valve. Any other possible solutions ??

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: High Pressure on relief valve

    any threaded holes under the valve body- then you can secure it to the frame

  5. #5
    Join Date
    Sep 2012
    Location
    greece
    Age
    32
    Posts
    5
    Rep Power
    0

    Re: High Pressure on relief valve

    I have already done that . I am thinking to change the whole supply tube from 18mm to 1/2 inch so that the volume of the liquid to be smaller when it comes to the relief valve. What do you think about that ?

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: High Pressure on relief valve

    do the 3 compressors have unloaders on them? with 6 evaps .each with solonoids on em how are you controlling the demand

  7. #7
    Join Date
    Sep 2012
    Location
    greece
    Age
    32
    Posts
    5
    Rep Power
    0

    Re: High Pressure on relief valve

    yeap, the compressors have unloaders.About the chambers, each chamber has an ON/OFF switch. When the switch is ON and if the temperature is below the thermostat set, the evaporation fans start and the solenoid valve opens. If the low pressure rises below a limit then a compressor starts (maybe some other of the three compressors already working, depanding on how many chambers are ON). In other words, thedemand is controlled by low pressure switches. (Sorry for my poor english )

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: High Pressure on relief valve

    normally if pipes are clamped using hydrazorb clips then that can hold pipes rigid without allowing for expansion/contraction, are the solonoid coils flared or brazed?

  9. #9
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: High Pressure on relief valve

    Chris, do you by any chance have a picture of the set up. This may help with ideas.

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: High Pressure on relief valve

    Put some length of vertical pipe capped at top, just before relief valve. That will make some pocket for gases which will eventually act as damping for liquid hammers.

  11. #11
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: High Pressure on relief valve

    What kind of expansion valves are you using, and how far from the expansion valves are the solenoid valves?

    Just a wild guess, but it sounds like the distance from the solenoids to the TEV's might be too long and once the thermostat closes the solenoid the whole pipeline is pumped dry, and once it opens again the liquid has a long way to travel before it hits the TEV, causing vibration.

    some more info would be nice
    -Cheers-

    Tycho

  12. #12
    Join Date
    Jan 2008
    Location
    England
    Posts
    25
    Rep Power
    0

    Re: High Pressure on relief valve

    Have in the past brazed in a 1/4 copper bypass line around main solenoid and then opened 1/4 solenoid to allow pressure across gently before opening main valve after a delay.