    Oct 2008
    newbury
    1,445
    correct me if i am wrong..
    but we have a U7 flashing on a MHI VRF. Is this something to do with the addressing as I 'fink' U7 means Unit 7 and the flashing means it's lost comms with the outdoor or something??
    TIA
    5,733
    Re: correct me if i am wrong..
    Not sure about the U7 code? But look on page 40 and it mentions I/U ?? (Indoor Unit Number)
    http://www.3dair.co.uk/DOWNLOADS_may...20&%20KXR4.pdf
    manchester
    5,707
    u-07 is indoor unit no 7 fault, check limit switch on the filter door, all fault codes are e numbers, had a triple system alarming on e01, checked outdoor unit, 240v on cond terminals ok turned out the some lanky git switched off 2 indoor spurs- units 12 ft up!!!- reset outdoor power and alarm cleared
    press check button on controller, push down to highlight error data, select number 7 unit to see the fault
    manchester
    5,707
    Oct 2008
    newbury
    1,445
    wireless remote. the run light flashes 3 times...
    manchester
    5,707
    compressor lock
    Oct 2008
    newbury
    1,445
    compressor lock
    all the other indoors run no problem and heat/cool ok..
    5,733
    The only reference to 3x red light flashes I could find is on page 14 of the manual (link in post #2)