    Swimming Pool Heat Pump Fault



    Hi everyone, I'm new to the forum so please point out if I make any mistakes or bend rules.

    I'm a Refrigeration/AC Mechanic that has been asked to check a friends FairLand Vertical Swimming Pool Heat Pump. I haven't much (if any) experience with these things. The unit runs for @ 10 mins then cuts out on 'PPO6 - Compressor Outlet Overload Protection'. Unit is charged with R407C. On my manifold Gauges I am getting a compressor suction pressure of between 50-60psi and a compressor discharge pressure of 140-150psi (seems a little low for 407C). However the discharge pipe temperature (before and after Diverter valve) is @ 95'C! Fan runs OK, Pool Pump is OK and Pool water filter is not blocked. The Diverter valve seems to be in the correct position as compressor discharge gas is flowing directly into the heat exchanger/condenser. Ice is forming on the distributor pipes that feed the evaporator coil. Do these running pressures sound correct? I'm not convinced it's short of gas, but then can't explain why it's cutting out on Compressor Discharge temperature Protection either. Is there some hidden gauze/filter at the heat exchanger inlet that could be blocked that I've overlooked, causing poor water flow in the Heat Exchanger? Any help with what common faults cause this condition would be greatly appreciated.

    Many thanks in advance



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Swimming Pool Heat Pump Fault

    Hi Smartus and welcome,

    95ºC sounds a bit on the high side.
    Normally when not enough refrigerant get back to the compressor the discharge temperature start to creep up.
    Could be due to a lack of refrigerant but also because something isn't right on the evaporator side of things, like lack of airflow through the coil for example.
    Best thing to do would be to hook your gauges up to the system and see what the sub cooling and superheat are doing.

    Happy hunting,


  3. #3
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: Swimming Pool Heat Pump Fault

    Check as viking suggests, you could be right with poor water flow, is the evaporator air cooled? If so check it's not blocking up.

    al
    Mostly found in the southern part of this green and pleasant land.

  4. #4
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: Swimming Pool Heat Pump Fault

    welcome to the forum by the way)
    Mostly found in the southern part of this green and pleasant land.

  5. #5
    Join Date
    Apr 2014
    Location
    Australia
    Posts
    2
    Rep Power
    0

    Re: Swimming Pool Heat Pump Fault

    Thanks for the welcome guys and thanks for the advice.

    Regarding the Subcooling I can get a gauge line on between the Heat Exchanger/Condenser outlet and the Electronic Expansion Valve so it's impossible to check that. I'll check the Superheat and see what I'm getting and see what I'm getting. Although that'll be on the suction pipe rather than the Evap outlet as there aren't any other system access points. I'll clean out the Evap as well and check that it's nice and clean before doing anything else. I'll let you know how I go...

    Cheers.

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Swimming Pool Heat Pump Fault

    Hi Smartus
    check sub cooling with a digital thermometer and compare with discharge pressures SDT.
    High discharge temp.. faults could indicate a tied compressor and bypassing internally, the internal relief could have let go previous and is still leaking. 150 psig discharge nominal 10 bar SDT +30' C ish
    Welcome to the forum by the way.

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Swimming Pool Heat Pump Fault


  8. #8
    Join Date
    Jan 2009
    Location
    Canary Islands
    Age
    74
    Posts
    144
    Rep Power
    16

    Re: Swimming Pool Heat Pump Fault

    Hope you have this sorted by now! Sounds as though it was water flow - possibly too slow.
    All the pool heating systems I install always have a by-pass valve so that the water flow through the heat pump can be adjusted. It's amazing the difference even small adjustments can make.
    With new machines, and (hopefully!) correct refrigerant charge and superheat, I balance the water flow by monitoring discharge pressure and current drawn by compressor. Can take a few return visits, but I can a good starting point this way.
    Buen suerte, Graham
    en boca cerrada no entran moscas

  9. #9
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Swimming Pool Heat Pump Fault

    You could also check the discharge outlet thermistor for calibration

  10. #10
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Swimming Pool Heat Pump Fault

    how would he have a suction press of 50-60 and a discharge of 140 with no power to it??
    Quote Originally Posted by MaryD View Post
    Did you check if the circuit breaker has been tripped? or the fuse has blown? Or call a Heat pump repair expert you can check this out for info's

  11. #11
    Join Date
    Jul 2004
    Location
    NE England
    Age
    56
    Posts
    81
    Rep Power
    21

    Re: Swimming Pool Heat Pump Fault

    That would be some call out. Vegas to Australia!!!!

  12. #12
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Swimming Pool Heat Pump Fault

    just another gimp trying to promote a buisness, which is pointless because not many people will see it- better off walking round vegas naked wearing a bill board!

  13. #13
    Join Date
    Jul 2014
    Location
    United States
    Age
    34
    Posts
    2
    Rep Power
    0

    Re: Swimming Pool Heat Pump Fault

    Did you check if the circuit breaker has been tripped? or the fuse has blown? Or call a Heat pump repair expert.

  14. #14
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,492
    Rep Power
    24

    Re: Swimming Pool Heat Pump Fault

    Quote Originally Posted by MaryD View Post
    Did you check if the circuit breaker has been tripped? or the fuse has blown? Or call a Heat pump repair expert.
    Dumb.........

  15. #15
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,645
    Rep Power
    23

    Re: Swimming Pool Heat Pump Fault

    Quote Originally Posted by MaryD View Post
    Did you check if the circuit breaker has been tripped? or the fuse has blown? Or call a Heat pump repair expert.
    There is this nifty thing between your ears, when you use it you avoid sounding like you have a stiff breeze going between said ears, do pray tell how you'd get the pressures he is giving with no power?

    Perhaps you'd best step out and let the adualts talk and the guys with training, I'm glad your an eager sales man but this isn't the place for you!