Results 1 to 9 of 9
    Apr 2014
    41
    5
    Williams WBC30 - Blast Chiller
    I have a faulty compressor on a Williams Stand-up Blast Chiller . . . replacement comp is £400, replacement unit is nearly £4000!! Obviously they want the comp changing, I don't work on these very often and I didn't get the chance to have a good look at it, but the discharge pipe from the comp is brazed in, but how the hell do you get to it? Does the condenser unit pull out?
    11,025
    Re: Williams WBC30 - Blast Chiller
    Can you not cut the pipe somewhere more convenient?
    Apr 2014
    41
    5
    Hi Brian, like I say, I didn't get the chance to have a good look at it, but from I saw, the discharge pipe goes to a T-piece, it splits between going to the condenser coil and a solenoid valve, which I presume is for some kind of hot gas de-frost. The problem is that it is all very compact, I could barely see the discharge joint, I just wondered if the the actual condenser unit pulls out some how?
    Oct 2007
    manchester
    5,639
    45
    braze some pipe onto the new compressor before you fit it- check the capillary line isnt run inside the suction line- youll have fun if you chomp it and find a capillary inside- been there done that! haha
    Apr 2014
    41
    5
    Thanks, the suction looks rota-lock type fitting, but the discharge is brazed and looks a pig, I can hardly see it, how the hell can I unsweat it and re-braze it? I'm sure the condenser unit slides out some how?
    Oct 2007
    manchester
    5,639
    45
    undo suction rotorlock, unbolt comp, slide it away to allow space to either cut the pipe with a hacksaw right near the pot- then it can be unsweated and refitted( ensure no swarf gets in the pipework- or cut it with tube cutters
    Apr 2014
    41
    5
    Thanks for that, I had another look at it today, the condenser unit underneath is a l'unite hermetique, I'm sure I remember that years ago these used to pull out but this looks different, will have to wait and see, comp on order
    3,856
    I have some wire cutters like these, http://www.screwfix.com/p/c-k-cable-cutter-210mm/51831
    they will cut through copper pipe when you cant get a pipe cutter in. You could potentially chop the discharge pipe off the comp and when its out the way unsweat it. If you have an oxy acetylene then i expect you could quickly braze it back in the new compressor. You may need to file off some braze to get it to fit in the hole.
    I use yellow dusters soaked in water to prevent heat from brazing damaging anything, also have a small sheet of ali that makes a good heat shield. If there is not enough room then do as others have said and braze a stub on it to reach to where its easier.
    Apr 2014
    41
    5
    Thanks for that monkey spanners