    How much liquid?



    Hey all,

    on Friday a tech charged a AC system with 15kg of 410a . He charged in liquid straight into the suction and discharge of a cope land scroll compressor.. The compressor doesn't have a crankcase heater. We have left the comp off all weekend. What percentage of liquid / vapour can we expect in a system like this.i realise it will depend on the saturation/ ambient condition. The system doesn't pump down when it cycles off any way so even under normal running conditions I would expect the refrigerant to migrate to the colder outdoor unit. Should we have any worries a bout starting this compressor on Monday?


    The more I learn the less I know......

  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: How much liquid?

    if your charging a system, its unusual to get the full charge in without running the system, as for firing it up on monday it will be alright

  3. #3
    Join Date
    Apr 2008
    Location
    Tasmania
    Posts
    218
    Rep Power
    17

    Re: How much liquid?

    Sucked in all 15kgs via vacuum. Long pipe run.
    The more I learn the less I know......

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: How much liquid?

    Turn it on, if sounds funny turn it off again and wait a bit before turning back on.
    Mostly found in Oxfordshire, UK :)

  5. #5
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: How much liquid?

    .

    As said above it should be alright.
    You say it does not pump down so it will be in the same condition
    it would be if the compressor cycled off for what ever reason.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  6. #6
    Join Date
    Feb 2009
    Location
    United States
    Age
    65
    Posts
    10
    Rep Power
    0

    Re: How much liquid?

    You could gently torch the side of the compressor and feel the level of liquid in it just for fun. If it is full of liquid, heat it for awhile. Then fire it up, shut it off, wait then do it again. It will be ok. When scrolls first came out, they did not put heaters on any of them, saying it could pump rocks. Then they started putting heaters on.

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: How much liquid?

    Hi Drew.
    Irrespective if it is a 1 Kw system or a 1 mega watt system, fit a sump heater to the compressor.