    Apr 2008
    Tasmania
    214
    12
    How much liquid?
    Hey all,
    on Friday a tech charged a AC system with 15kg of 410a . He charged in liquid straight into the suction and discharge of a cope land scroll compressor.. The compressor doesn't have a crankcase heater. We have left the comp off all weekend. What percentage of liquid / vapour can we expect in a system like this.i realise it will depend on the saturation/ ambient condition. The system doesn't pump down when it cycles off any way so even under normal running conditions I would expect the refrigerant to migrate to the colder outdoor unit. Should we have any worries a bout starting this compressor on Monday?
    The more I learn the less I know......
    Oct 2007
    manchester
    44
    5,707
    Re: How much liquid?
    if your charging a system, its unusual to get the full charge in without running the system, as for firing it up on monday it will be alright
    Apr 2008
    Tasmania
    214
    12
    Sucked in all 15kgs via vacuum. Long pipe run.
    44
    3,800
    38
    Turn it on, if sounds funny turn it off again and wait a bit before turning back on.
    May 2012
    54
    1,325
    30
    As said above it should be alright.
    You say it does not pump down so it will be in the same condition
    it would be if the compressor cycled off for what ever reason.
    Rob
    Feb 2009
    United States
    59
    10
    You could gently torch the side of the compressor and feel the level of liquid in it just for fun. If it is full of liquid, heat it for awhile. Then fire it up, shut it off, wait then do it again. It will be ok. When scrolls first came out, they did not put heaters on any of them, saying it could pump rocks. Then they started putting heaters on.
    Auckland
    68
    3,362
    32
    Hi Drew.
    Irrespective if it is a 1 Kw system or a 1 mega watt system, fit a sump heater to the compressor.