    We use glycol from heat recovery for the cold store (-21C) floor. Can someone let me know what is the recommended glycol temp required. I don't want to add unnecessary heat load.
    Jan 2006
    Croatia
    2,116
    23
    Re: Cold Store Floor Temperature
    Hi, Tecknic
    Welcome to RE forums
    Quote Originally Posted by Tecknic View Post
    We do not know what type of floor insulation you have ... so the best and only way is to control glycol temperature in return pipe.
    It must be above 273,15 K .... 283 K within return pipe is not to high, but believe me, even if you add some unnecessary load to your evaporator it is much cheaper then frozen soil under cold store floor.
    Best regards, Josip
    Sep 2009
    Iran
    430
    11
    best and safe one +4 C up to +6 C