    Apr 2012
    Iraq
    35
    623
    split ac unit different capacity value
    how r u guys
    im confused about the info on the name plate of different split ac unit
    as example when u check the heating and cooling capacity u will find the cooling is 6740 watt
    and heating is 7320 watt
    also u can check in other split ac unit that the current
    are different or same in cooling or heating
    what is the reason
    Feb 2007
    2,473
    Re: split ac unit different capacity value
    OK,
    If we go back to fundamentals, the heat output from the condensor=the cooling duty of the evaporator + the heat added by the compressor.
    Therefore the the capacity in heating mode will be higher than the capacity in cooling mode (heat=cooling+compressor).
    In modern A/C systems, in order to optimise performance, the discharge pressure is elevated during the heating cycle. Higher pressure = higher temperature.
    If you look at the spec of a compressor you will see that higher discharge pressure=higher current draw.
    Clear as murky waters!
    Apr 2012
    Iraq
    35
    623
    ok
    thank u for the detailed explain
    i red in the college some of what u mentioned
    ok
    why in some mini split heat pump unit the current for heating is lower than in cooling
    as example
    Feb 2007
    2,473
    As they have chosen to keep the duties the same in both modes they will be able to run the compressor at a reduced duty whilst in heating mode. (If we follow the same principle as above)
    moideen's Avatar
    Apr 2008
    u.a.e
    49
    412
    I think they (konka) have done some mistakes on writing heating capacity. It is simple 2 ton system. Look at the power input, it is different. I googled for the catalogue, no found.this is Chinese made,there is chance for mistakes..........
    Apr 2012
    Iraq
    35
    623
    Quote Originally Posted by moideen View Post
    thank
    what about this unit
    its LG Korean made