    split ac unit different capacity value



    Hi
    how r u guys
    im confused about the info on the name plate of different split ac unit
    as example when u check the heating and cooling capacity u will find the cooling is 6740 watt
    and heating is 7320 watt




    also u can check in other split ac unit that the current
    are different or same in cooling or heating
    what is the reason
    Last edited by kefah; 04-04-2014 at 11:46 PM.



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: split ac unit different capacity value

    OK,
    If we go back to fundamentals, the heat output from the condensor=the cooling duty of the evaporator + the heat added by the compressor.
    Therefore the the capacity in heating mode will be higher than the capacity in cooling mode (heat=cooling+compressor).

    In modern A/C systems, in order to optimise performance, the discharge pressure is elevated during the heating cycle. Higher pressure = higher temperature.
    If you look at the spec of a compressor you will see that higher discharge pressure=higher current draw.

    Clear as murky waters!


  3. #3
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: split ac unit different capacity value

    ok
    thank u for the detailed explain
    i red in the college some of what u mentioned
    ok
    why in some mini split heat pump unit the current for heating is lower than in cooling
    as example

  4. #4
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: split ac unit different capacity value

    As they have chosen to keep the duties the same in both modes they will be able to run the compressor at a reduced duty whilst in heating mode. (If we follow the same principle as above)

    Last edited by The Viking; 05-04-2014 at 11:11 AM.

  5. #5
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    412
    Rep Power
    22

    Re: split ac unit different capacity value

    Quote Originally Posted by The Viking View Post
    As they have chosen to keep the duties the same in both modes they will be able to run the compressor at a reduced duty whilst in heating mode. (If we follow the same principle as above)

    I think they (konka) have done some mistakes on writing heating capacity. It is simple 2 ton system. Look at the power input, it is different. I googled for the catalogue, no found.this is Chinese made,there is chance for mistakes..........
    Last edited by moideen; 05-04-2014 at 07:04 PM.

  6. #6
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    623
    Rep Power
    17

    Re: split ac unit different capacity value

    Quote Originally Posted by moideen View Post
    I think they (konka) have done some mistakes on writing heating capacity. It is simple 2 ton system. Look at the power input, it is different. I googled for the catalogue, no found.this is Chinese made,there is chance for mistakes..........
    thank
    what about this unit
    its LG Korean made