    mitsubishi msz-ga35va ac indoor unit



    Hi.
    Operation light is constantly flashing on indoor unit. No definate sequence, just flasing constant. On start up fan motor operates for couple of minutes then stops and operation light flashes.? Any opinions appreciated.
    Thanks



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: mitsubishi msz-ga35va ac indoor unit

    limit switches on the louvres

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: mitsubishi msz-ga35va ac indoor unit

    POWER lamp Abnormal point
    (Failure mode) Condition Correspondence
    Not lighted Normal — —
    1-time fl ash every
    0.5-second
    Room temperature
    thermistor
    The room temperature thermistor short or
    open circuit is detected every 8 seconds during
    operation.
    Refer to the characteristics of the room temperature
    thermistor (10-7.).
    2-time fl ash
    2.5-second OFF
    Indoor coil
    thermistor
    The indoor coil thermistor short or open circuit
    is detected every 8 seconds during operation.
    Refer to the characteristics of the main indoor coil thermistor,
    the sub indoor coil thermistor (10-7.).
    3-time fl ash
    2.5-second OFF Serial signal The serial signal from outdoor unit is not received
    for a maximum of 6 minutes.
    Refer to 10-6. "How to check miswiring and serial
    signal error".
    11-time fl ash
    2.5-second OFF Indoor fan motor
    The rotational frequency feedback signal is not
    emitted during the 12 seconds the indoor fan
    operation.
    Refer to 10-6. "Check of indoor fan motor".
    12-time fl ash
    2.5-second OFF
    Indoor control
    system
    It cannot properly read data in the nonvolatile
    memory of the indoor electronic control P.C.
    board.
    Replace the indoor electronic control P.C. board.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: mitsubishi msz-ga35va ac indoor unit


  5. #5
    Join Date
    Apr 2014
    Location
    ireland
    Posts
    2
    Rep Power
    0

    Re: mitsubishi msz-ga35va ac indoor unit

    Room temperature thermistor failure.
    replaced and back in operation.
    cheers