    first I want to say hello to all people from here. I have a problem with a ultra freezer. We changed the compressor for low freezer with a new one. we filled with R508B and now we have some problems with oil returns. I read on this site about a solution: to add some Pentane. But nobody says how much . Maybe some one can tell me this thing and what method he use to do this.
    Thank you and sorry if I say some old already things.



  2. #2
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Problem with oil returns using R508B

    could you give more information about:
    compressor model
    room temperature
    oil type you used
    describe your system.
    might I can help you.

  3. #3
    Join Date
    Apr 2014
    Location
    Romania
    Age
    42
    Posts
    8
    Rep Power
    0

    Re: Problem with oil returns using R508B

    Hello, the model is AEZ2411Z, the temperature of the room is around 16-18 Celsius, the type of the oil is the one from the compressor, I didn't put extra oil but when I changed the old compressor with the new one I didn't take off the entire old oil. The system is a ultra freezer in cascade from GFL Germany.
    I wait your help . Have a nice day

  4. #4
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Problem with oil returns using R508B

    ecumseh AEZ 2411 Z , hermetic compressor, LBP 220/240V -R404A - R507 -R407B -
    Displacement : 7.6 cm³
    Net weight : 10.2 Kg
    Oil charge : 250 cm³
    Oil type : P.O.E /
    Expansion device : Capillaire/Détendeur
    Capillary/Exp° valve
    Cooling :Forced
    Windings resistances at 20° C
    Main Winding : 6.8 Ohms
    aux. / Auxiliary Winding : 30.2 Ohms
    Intensité / Current
    nom. / Rated current RLA : 2 A
    max. / Max current : 3.1 A
    dém. / Start current LRA : 13 A
    Ap. Electrique / Electrical equipment : CSIR
    Protecteur / Overload : MRP56AMK
    Temporisation / Time Check : 7.5s - 14s / 9.4 A
    T° ouverture / Opening temp.: 105° C
    fermeture / Closing temp. : 61° C
    Option / optional : T0599
    Relais Intensité / Current relay : MTRP0027
    enclenchement / Pick up : 6,2A
    déclenchement / Drop out : 5,25A

    these information i got from internet .
    you see it works with P.O.E oils and your old compressor might works with mineral oils.

    2) I wonder , how you find the oil is not return to you compressor.

  5. #5
    Join Date
    Apr 2014
    Location
    Romania
    Age
    42
    Posts
    8
    Rep Power
    0

    Re: Problem with oil returns using R508B

    Hello, thank you for your answer.
    First i want to say that I use this equipment for -85 Celsius, and now my lowest temperature is around -60 Celsius. This is the reason that I think my oil is not returning.
    Best regards

  6. #6
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    400
    Rep Power
    18

    Re: Problem with oil returns using R508B

    Use of a microfibre oil separator is suggested ....arrest the oil going forward rather than worry about bringing it back from evaporator. Besides the suction gas velocity at -60 deg c v/s -85 deg c could also play part due to suction pipe diameter.

    Dd koranne

  7. #7
    Join Date
    Apr 2014
    Location
    Romania
    Age
    42
    Posts
    8
    Rep Power
    0

    Re: Problem with oil returns using R508B

    Quote Originally Posted by D.D.KORANNE View Post
    Use of a microfibre oil separator is suggested ....arrest the oil going forward raither than worry about bringing it back from evaporator. Besides the suction gas velocity at -60 deg c v/s -85 deg c could also play part due to suction pipe diameter.

    Dd koranne
    hello Koranne, thank you for your advice.
    The part with the microfiber oil separator is very nice, I will try this.
    About the second part of your message, I don't understand very well what you mean. Maybe you can say more explicit about that?
    Thank you

  8. #8
    Join Date
    Aug 2004
    Location
    Holland
    Posts
    55
    Rep Power
    20

    Re: Problem with oil returns using R508B

    If you only reach -60, than indeed oil in the evaporator may be part of the problem.
    standard poe oil has a viscosity of 32 meaninf that T - 60 or lower it will be thick like sirup, in combination with the very low gasflow at these temperature oil return will become a problem.
    In r508b datasheet there is a recomendation to ad mineral oil to ad in increased oil return.

    on the other hand charge in these systems is very critical.
    you should take readings in suction pressure, and superheat of suction line straight after evaporator, and make sure it it within the range to reach -80 or lower.

  9. #9
    Join Date
    Apr 2014
    Location
    Romania
    Age
    42
    Posts
    8
    Rep Power
    0

    Re: Problem with oil returns using R508B

    Quote Originally Posted by coolman View Post
    If you only reach -60, than indeed oil in the evaporator may be part of the problem.
    standard poe oil has a viscosity of 32 meaninf that T - 60 or lower it will be thick like sirup, in combination with the very low gasflow at these temperature oil return will become a problem.
    In r508b datasheet there is a recomendation to ad mineral oil to ad in increased oil return.

    on the other hand charge in these systems is very critical.
    you should take readings in suction pressure, and superheat of suction line straight after evaporator, and make sure it it within the range to reach -80 or lower.
    Hello,
    Thank you for being agree with me about the oil return problem. Do you know something about th ePentane solution? How to fill with this and how much? Or do you have other advice about solve this?

  10. #10
    Join Date
    Aug 2004
    Location
    Holland
    Posts
    55
    Rep Power
    20

    Re: Problem with oil returns using R508B

    as stated in the documentation R508b adding mineral oil can have a possitive effect on oil return.
    same happens with R438b a drop in for r22, here we add about 30% of mineral oil ie gs3, in ypur case it contains 250cc so ad about 70 cc mineral oil.

    that is if there is a oil buildup in evaporator.
    do your reading suction pressure/superheat discharge/pressure/temp/sub cooling support these findings

    if there is oil buildup, you should end up with low superheat and low discharge.

  11. #11
    LowTemp-10F's Avatar
    LowTemp-10F Guest

    Re: Problem with oil returns using R508B

    When you change the low stage compressor, did you change the oil separator and flush the system?