Results 1 to 4 of 4
  1. #1
    Join Date
    Nov 2013
    Location
    England
    Age
    42
    Posts
    33
    Rep Power
    0

    Fujitsu vrf indoor / controler address



    We have been asked to re install a fujitsu vrf system that had been de gassed & removed by others . 8 indoor units & 4controllers have been re positioned ,
    I'm after some advice on the addressing of the system ? Do indoors someway need matching to the controlers via the sw 10,9,8,7,6 dials ? The controlers have ds 1 switches 1-6 ? Do these dips need setting to correspond with the units it's controlling ?

    It's our 1st fujitsu vrf system so any help would be grateful

    Thanks



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Fujitsu vrf indoor / controler address


  3. #3
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Fujitsu vrf indoor / controler address

    Its V series)
    I think he got V2, don't have time to look manuals(
    But you need to clear all address and make new auto address operation, after that programming wired controllers.

  4. #4
    Join Date
    Nov 2013
    Location
    England
    Age
    42
    Posts
    33
    Rep Power
    0

    Re: Fujitsu vrf indoor / controler address

    Thanks for the replies lads , helpful manual , all we needed to change was sw10 for the controlers , as all the units were kept on there original systems & positions !!

    All sorted and running thank you !!