    Question MYPRO cpIII communication problem



    compressors are Mayekewa screw type with Mypro cp3

    In a scenario
    Compressors will work in Auto-stage
    and it is required to monitor compressors in a special SCADA software, just to monitor

    Among with various data related to sytem, it is intended to collect the data of compressors to a device(basically a PLC) which communicates with RS485. The connection with pc will be formed over this device.

    Problem:
    a collegue insists the RS485 protocols are being used by CP3 and this device are "different"!
    Also I have encountered a similiar topic which mentions Mypro CP3 and PLC connection is not feasible though imho the answers were a bit not complete(thus i brought this topic).

    and the information related to CP3 on internet is very very limited.

    Any ideas or information? Or can you at least tell me why i can not take input from CP3 to PLC (recall: both use RS485)

    or any different ideas for monitoring?

    Thank you for help



  2. #2
    persim's Avatar
    persim Guest

    Re: MYPRO cpIII communication problem

    Hi
    No problem to communicate with a CP III have done this already in 2001, latest project when I worked
    with communication to 5 CP III at ones function fine. I'm using a SAIA Burgess PCD3.M5340 and using
    the RS485 port. The communication with the CP III is thoug based on ASCII character transmttion.

    Example:
    To read values from a CPIII you need to send the following string:
    STX,_,A1,A2,'04RDDT',_,_,ETX

    STX start of text ASCII 2
    _ space (blank)
    A1A2 Adress of CP II 1..31) if it is 1 A1=0 A2=1
    04RDDT fixed ASCII characters
    ETX End of text ASCII 3

    The returning result is a text string consisting of 276 characters which you the have to split up

    Best regards

    If you would leave your mail adress I could give you the doc..
    Last edited by persim; 06-09-2014 at 04:58 PM.

  3. #3
    Join Date
    Nov 2014
    Location
    lamdong
    Age
    35
    Posts
    1
    Rep Power
    0

    Re: MYPRO cpIII communication problem

    hi all
    i use the PLC s7 300 to communication with mypro cp3 .I read manual CPIII so i use the format:
    STX,SPX,A1,A2,0,4,R,D,D,T,_,_,SPC,SPC,SPC,ETX
    it is correctly ?