    Unit Cooler Ice Up



    Hi, Everyone. I faced some problems of my project.
    I installed a set of Compressor and Condenser c/w 2 units of different model of unit coolers for 2 units of coldroom. Below show the model of items that installed:

    Compressor: Bitzer 4EC-6.2Y-BJ Semi Hermetic Compressor
    Eden EFGP 0343.51 RB G4 Condenser 34.3Kw
    Eden FEME 0450 G4 Unit Cooler 4.50Kw @ 6KTD c/w 3x300mm fan set (Temperature Require -2'c)
    Eden FEM 0492 G4 Unit Cooler 4.92 Kw @ 8KTD c/w 1x300mm fan set (Temperature Require 3'c)

    The problems that i faced are when the Coldroom A reached -2'c, Coldroom B's unit cooler will ice up.
    May I know what's wrong of the unit cooler happened? Can any one could help and assist to solve this situation.

    Thanks and Best Regards.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Unit Cooler Ice Up

    To reach your target set points of -2C and +3C, both units will need to evaporate below freezing, therefore, it is normal for the indoor units to ice up. You should install a defrost system to both units.

    How are you controlling the temperature in the +3C space? do you have an EPR or LLSV fitted?

  3. #3
    Join Date
    Apr 2013
    Location
    Malaysia
    Posts
    14
    Rep Power
    0

    Re: Unit Cooler Ice Up

    Hi, Thanks for your reply.
    The both systems installed defrost system, it work normal 12 months previous and this problem occur this month.
    In the pass 12 months, defrost every 6 hours but now have to defrost every 2 hours.

  4. #4
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Unit Cooler Ice Up

    is it 2 separate systems?
    do you have ice on suction side of comp.( check expansion valve).
    what is the definitional temp. on both units.?
    check evaporates air flows.
    are your doors sealed ?

  5. #5
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    567
    Rep Power
    24

    Re: Unit Cooler Ice Up

    Hi hong
    I would be checking the door seals. Sounds like there is a lot of outside air getting in and this would be fairly humid I would expect given where you are.
    A bit more information about the system components would also be helpful (see Franks post).
    Have you checked the charge, are the LL driers blocked, is the condenser blocked.
    Paul
    Born to fish, forced to work

  6. #6
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    770
    Rep Power
    19

    Re: Unit Cooler Ice Up

    hi , can I take it you have liquid solenoids on both systems ? if you have, then you could have liquid line no1 going to cond, unit no 2 so you would end up with one unit trying to pump down both systems into one unit?= sedgy