Results 1 to 11 of 11
    Dec 2008
    chapeco
    Angry recovery rotors Sabroe 202
    Hello, Friends
    I'm having trouble Sabroe 202 in rotors station laps defects in bearings, but how do I need to recover?
    Metallization or hard-chrome
    Jul 2007
    Czech
    61
    374
    Re: recovery rotors Sabroe 202
    Hi Diego, plating no, you have to grind down and pressed a new ring.
    3,357
    Quote Originally Posted by diego palma View Post
    Hello, Friends
    Diego, do you have a picture of worn area as well as dimensions ?
    Makes it easier to understand problem
    Dec 2008
    chapeco
    Rotor with severe wear.
    Original measure 104.90 mm
    Measurement found in 104.77 mm rotor
    How do I recover the rotor with hard-chrome plating or
    3,357
    [/QUOTE]
    Diego, I think hard chrome is OK as maximum thickness usually 0.5mm maximum.
    Josef suggests sleeves, which would be heated to put on then ground. Need to be hardened before though, maybe nitrided.
    Not sure why Josef prefers sleeves?
    Auckland
    74
    3,357
    37
    I agree with Ranger1, I have tried all the above. It comes down to the machine shop that is doing the job though. Critical applications I would tend towards a new set of rotors from factory, and be able to sleep peacefully at night.
    magoo
    Jul 2007
    Czech
    61
    374
    Thank you gentlemen, RANGER1, you are right, little damage chrome, chrome great damage is a problem. Magoo, restful sleep rotors are new.
    Jan 2006
    Croatia
    68
    2,263
    31
    Hi, diego palma
    In the past we had a similar problems with damaged rotors and sometimes with end covers too. All repairs were successful, some compressors are running still.
    We used to repair rotors to nominal size and use original slide bearings, nowadays are available thermal spray repairing procedures like:
    Flame spraying
    Plasma spraying
    HVOF (High Velocity Oxygen Fuel Spraying)
    Arc Spraying
    of course, the best is to ask material thermal spray specialist which procedure is the best in your case ... I do believe you can solve it without any problem ... of course the most critical procedure is grinding of shaft bearing shoulder to nominal size for bearing.
    Here is a link to see the procedure (found this on www ... this company is doing all reparations for us here in Croatia:
    http://www.youtube.com/watch?v=ecEVghstNRc
    Hope this is of some help to you.
    Best regards, Josip
    3,357
    Diego,
    Repairs aside, in everyone's interest to find out why serious wear on journals occurred.
    Unless there was a filter or safety protecting it that failed?
    Normally hard to kill if all safeties working!
    Dec 2008
    chapeco
    Hello, we recover the rotor by plating with stainless steel and most hard chromium more balancing assembly and compressor rotors Inc. All rights reserved with the original measure
    May 2003
    Vietnam
    65
    The most modern way is right alloy brazing with induction heating or laser.
    Truc
