    R600a Fridge



    Hello all, I am after a bit of info on a domestic fridge Skandiluxe (Similar to Vestfrost) please?
    I have fitted a new compressor & have weighed in the 35grams (on ID plate) of R600a (Isobutane) & have very high Superheat & a warm suction line when the cabinet is at its design temp of + 2°C
    Test figures are-

    Ambient temp 30°C Humidity 50% Compressor is only drawing 170mA which is well under the Danfoss design chart.


    Evap. cabinet temp 0°C (32°F)
    Low side saturation temp -19°C (-26kPa) (-7.6"hg)
    Suction line temp of + 31°C (88°F)
    SH 50 °K (90°R)

    Condenser temp 44 °C (111°F)(outside of cabinet, inside wall condenser)
    High side saturation temp. 46°C (115°F) (525kPa) ( 76psig)
    Liquid line temp 43°C (109°F)
    SC 3°K (5.4°R)

    I am worried that the compressor may run too hot when the hot weather comes with the high SH? Can I get any expert opinions please? Do I need to add more charge?
    PS it is very hard to weigh in 35grams with a STD 1/4" hose hanging on a small R600a can.
    PS This section of fridge is not the freezer part. (it has completely dual systems)

    Thanks in advance for your help. Leigh



  2. #2
    Join Date
    Aug 2009
    Location
    Portugal
    Posts
    20
    Rep Power
    0

    Re: R600a Fridge

    Hi,try adding in a little more gas. Did you fit the same type of compressor?

  3. #3
    Join Date
    Nov 2007
    Location
    Australia
    Age
    69
    Posts
    18
    Rep Power
    0

    Re: R600a Fridge

    Thanks for your reply Sacoolman,
    The new compressor was supplied by the fridge dealer for free (sort of extended warranty-customer relations) to help us out & sat around for a while, It is bit smaller (3.86cc) Danfoss TLES-4KK-2 R600a against the original VOE HYV44AA 0038 R600a (4.38cc)
    I did add a few more wiffs of gas one day & it seemed to play around with the thermostat badly.
    I took the suction down to -24°C (-11°F) -41kPa (-12"hg) (-0.4bar) as suggested by some old posters on a search on this forum & the suction into the compressor frosted badly & the thermostat didn't cycle properly, the cabinet went down to about -4° after an hour even with the thermostat set on low (No. 1 on the dial)
    Seems very hard to get the charge & SH correct at cabinet design temp (operating) about 2°C.
    This fridge appears to be too efficient & working too good.
    Do we set a fridge (cooler only) different as apposed to a freezer & fridge combined?
    Sorry my experience has been mainly automotive AC.
    Thanks - Leigh

  4. #4
    Join Date
    Feb 2008
    Location
    devon
    Age
    46
    Posts
    15
    Rep Power
    0

    Re: R600a Fridge

    All the system I have looked at the comps always run hot.
    If you dont think the capilary has any blockage and you changed
    the drier add a few more grams and let it be.

  5. #5
    Join Date
    Apr 2014
    Location
    Pakistan
    Age
    32
    Posts
    3
    Rep Power
    0

    Re: R600a Fridge

    Hi
    U have same r600a type compressor

  6. #6
    Join Date
    Nov 2007
    Location
    Australia
    Age
    69
    Posts
    18
    Rep Power
    0

    Re: R600a Fridge

    Haven't had time to get back to the fridge yet, but I will play around with charge a bit, I think the humidity may of been playing around with the frost on the suction line, & I may lag the pipe a bit.
    Yes it is a R600a compressor but the one that the company supplied under a belated warranty claim for free is 13.5% smaller in capacity & after reading about capillary tubes & an inefficient compressor it seems as if the capillary may now need to be shorter or smaller to have the balance correct.
    Thanks for your help - Leigh