    Lightbulb Misleading error merrage



    Carrier Transicold Maxima 2
    Error message: hi press


    While helping out to a friend fixing a trailer, I was misled by the error message displayed on the control box.
    I have guided my friend to check all the pressure switches and wiring on the discharge side of the system with no luck.
    I felt a bit silly when the problem came out to be refrigerant shortage.
    As soon as the system was charged with refrigerant all started running perfectly.
    I could not obtain a service manual for this trailer or a circuit diagram, therefore I could not find out why the system was displaying hi press message while it was completely short of refrigerant.
    Any comments?

    Guner



  2. #2
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: Misleading error merrage

    It should have brought up a alarm code,and on the inside of the unit door is a sticker relating to what the codes refer to .

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Misleading error merrage

    Quote Originally Posted by Guner Edip Riza View Post
    Carrier Transicold Maxima 2
    Error message: hi press


    While helping out to a friend fixing a trailer, I was misled by the error message displayed on the control box.
    I have guided my friend to check all the pressure switches and wiring on the discharge side of the system with no luck.
    I felt a bit silly when the problem came out to be refrigerant shortage.
    As soon as the system was charged with refrigerant all started running perfectly.
    I could not obtain a service manual for this trailer or a circuit diagram, therefore I could not find out why the system was displaying hi press message while it was completely short of refrigerant.
    Any comments?

    Guner
    Just maybe the condenser fan failed or some other issue caused an High pressure situation and your PRV lifted?
    If fitted?
    Which would result in a High pressure fault being displayed (Manual reset required?) but the system being short of refrigerant!
    Just a guess mind!
    Grizzly

  4. #4
    Join Date
    Aug 2011
    Location
    Canada
    Posts
    160
    Rep Power
    15

    Re: Misleading error merrage

    High pressure is a catch all code. Several things can trigger it. Depending on which software revision you have it could be running in a vacuum for more than five minutes it will trigger a high pressure code. Or if the discharge air is reading higher than return air it will also trigger this code. Even turning the switch on and off too fast will give you high pressure.

  5. #5
    Join Date
    May 2011
    Location
    Romania
    Age
    40
    Posts
    84
    Rep Power
    13

    Re: Misleading error merrage

    The wire than comes from pc board goes thrugh hp then lp swich, that's why they have the same connector, no matter how you connect them the result is the same hi press alarm for hi pressure or vacum on low side.