    Expansion tank in closed loop systems



    Would someone be able to assist with set up information of closed loop system
    What is ideal pressure in bladder.

    Thanks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    75
    Posts
    11,192
    Rep Power
    60

    Re: Expansion tank in closed loop systems

    How tall is the building and is the vessel at the top or bottom of it?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Expansion tank in closed loop systems

    Brian,
    It's not a building but a new processing plant.
    It has one closed loop with tank on top of evaporative air cooler for screw compressor oil cooling.
    Water circulates through tubes in evaporative cooler, so has an expansion tank above it.
    Also a closed loop glycol system for process cooling. Expansion tank mounted on pump return line.


    Tanks supplied with 200kpa pressure, interested in how to determine pressure in expansion tank ie when system is off do you have it same pressure of what's in system or is it something to do with pump suction pressure while running or do we do nothing.
    Assume systems are fully primed & operational.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Expansion tank in closed loop systems

    you need to know the volume of the system to calc the vessel size and charge-

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Expansion tank in closed loop systems


  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Expansion tank in closed loop systems

    The bladder in the expansion vessel has to be at a greater pressure than your system so that it can absorb the circuit hydraulic expansion.
    What you need to do is calculate the maximum hydraulic expansion ( increase in pressure)
    If the circuit can't expand your pressure relief valve will pass.