    Daikin screw chiller with burst evaporator



    Hi All,
    We were asked to look at the following Daikin screw chiller, EWAD760C-XSC01. We found the system full with water, so one or more of the tubes is possibly leaking. Details on the evaporator refer it to a McQuay evaporator, 40271111.
    In the past we have repaired Carrier tubes with Elliot plugs (brass pin & plug). The problem we have is trying to find the tube size. I have searched manuals to no avail and the local Daikin dealer has informed us that the tube specs is "proprietary information".

    Would anyone have details of the tube specs/size for this chiller?

    Thanks in advance,
    F



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Daikin screw chiller with burst evaporator

    As it's already wet you might as well open it and measure the tubes, that way there won't be any mistake.
    Last edited by Brian_UK; 25-03-2014 at 09:50 PM. Reason: spelling
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    18

    Re: Daikin screw chiller with burst evaporator

    Hi
    couldnt agree more with brian .
    no mistakes ! open, messure,order,fit this way you actully save time and money !
    good luck
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

  4. #4
    Join Date
    Nov 2005
    Location
    Ireland
    Posts
    23
    Rep Power
    0

    Re: Daikin screw chiller with burst evaporator

    Hi Brian/Goshen,

    I was hoping that I would only have to give the customer one quotation to carry out the total repairs, instead of a quotation to reclaim the 2nd circuit, remove end-plates, etc, and then supply a 2nd quotation to repair.
    I guess that we will have to measure it up then.

    Thanks again for your replies,
    Fintan

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Daikin screw chiller with burst evaporator

    Understand your reasoning Fintan but it is out of your hands if the manufacturers won't give you the information. Let the customer know why your hands are tied.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: Daikin screw chiller with burst evaporator

    if the plugs weren't expensive i'd order a selection of sizes and sealant, used to get wedge type which cover a range of diameters, not sure of the supplier though. only tear down manual i could find:
    http://lit.daikinapplied.com/bizlit/...ts/7000066.pdf

    I'd go with Brian though if above not possible, quote to strip and isolate leaks, remember if coil is crushed then repair may not be possible, i wouldn't quote repair until i knew what damage was.
    Mostly found in the southern part of this green and pleasant land.

  7. #7
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Daikin screw chiller with burst evaporator

    Its very interesting job.

  8. #8
    Join Date
    Nov 2005
    Location
    Ireland
    Posts
    23
    Rep Power
    0

    Re: Daikin screw chiller with burst evaporator

    Thanks again for the replies and the link to the manual.

    On checking the water side, pieces of metal slag were found in the evaporator and between the pipes. There was no filter fitted to the system and this is how the leaks occurred. Our customer is going to chase the installer for a new evaporator.

    Thanks again,
    Fintan

  9. #9
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Daikin screw chiller with burst evaporator

    Thats a good idea)))