Thread: Cooling Load
    Feb 2014
    40
    10
    Cooling Load
    I am designing a HVAC system for a location off the coast of Nigeria.
    Along with the AHU there is chiller system which I am trying to size.
    To calculate the cooling load can I simply use the volume airflow multiplied by the density of air and the delta T? Or do I have to use the equation:
    Qc = ma(ho hs)
    My problem with the later method is whilst I have the db and wb of the outside conditions i only have the db of the supply conditions so pinning down the process line of the psychrometric chart is difficult.
    Would an acceptable solution be to estimate the %RH for the supply conditions?
    Any advice would be appreciated.
    Oct 2008
    newbury
    57
    1,380
    29
    Re: Cooling Load
    do you have a cooling load for the space already?
    Feb 2014
    40
    10
    Re: Cooling Load
    Well i have calculated it using the air flow, air density and delta T but i dont think that is correct???
    Is that a correct assumption
    Mar 2006
    Lancashire
    1,872
    22
    Re: Cooling Load
    Hi Chris, yes that is how I would do it.
    Q= m x cp x DT
    Marc
    Feb 2014
    40
    10
    Re: Cooling Load
    Thanks Marc,
    I was not sure if i should be using the enthalpies.
    Really appreciated.
    Chris