    Hey,
    Wanted to start a thread about getting ammonia out of a piece of equipment for service. Most guys I talk to talk about "pump down" meaning connecting the section to be serviced to the low side and have other compressors pull the NH3 out. But what if it is a single compressor system and it can't be pumped down?



  2. #2
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Ammonia pump down procedures

    Purge it to a water vessel.
    To make progress is never good enough, I want to do better and better and better

  3. #3
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Ammonia pump down procedures

    Hi.TF12

    Quote Originally Posted by TF12 View Post
    Hey,
    Wanted to start a thread about getting ammonia out of a piece of equipment for service. Most guys I talk to talk about "pump down" meaning connecting the section to be serviced to the low side and have other compressors pull the NH3 out. But what if it is a single compressor system and it can't be pumped down?
    just curious ... a piece of equipment for service is ....

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  4. #4
    Join Date
    Feb 2014
    Location
    USA
    Age
    37
    Posts
    23
    Rep Power
    0

    Re: Ammonia pump down procedures

    A compressor package
    Ammonia chiller skid
    And aren't there limitations on how much you dissolve in water?
    What do you do with the water?

  5. #5
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Ammonia pump down procedures

    Quote Originally Posted by TF12 View Post
    A compressor package
    Ammonia chiller skid
    And aren't there limitations on how much you dissolve in water?
    What do you do with the water?
    Do you have any restrictions on ammonia, water solutions on this site?
    The more water you use the likelyhood of smell is reduced.

    If you used an old 44gallon drum or similar,it could be moved to somewhere suitable on site & discarded.

    We use a small transfer compressor, so don't have to worry.

    If you have another NH3 system close you could connect a hose to it to empty package.

  6. #6
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Ammonia pump down procedures

    Quote Originally Posted by TF12 View Post
    A compressor package
    Ammonia chiller skid
    And aren't there limitations on how much you dissolve in water?
    What do you do with the water?
    More or less 50% - 50% in volume with the NH3 in liquid state
    You shall neutralize the hydroxid of ammonia since is alcalline solution with an acid solution to get PH=7.
    To make progress is never good enough, I want to do better and better and better

  7. #7
    Join Date
    Feb 2014
    Location
    USA
    Age
    37
    Posts
    23
    Rep Power
    0

    Re: Ammonia pump down procedures

    Tell me more about this transfer compressor. You mean to pump to another vessel like a recovery machine?

  8. #8
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Ammonia pump down procedures

    [QUOTE=TF12;293734]Tell me more about this transfer compressor. You mean to pump to another vessel like a recovery machine?[/QUOTE

    Yes we ave made our own.
    One is a large car or truck air con compressor belt driven.
    The other a larger unit with suction trap. Both single phase motors.
    Yes both used for ammonia, regular oil changes. Larger unit o rings changed to neoprene.
    Just use ammonia hoses to transfer to other part of system like liquid receiver.