    Hi,
    I am thinking of using a TXV to control cooling using cold water or cold air for my pilot project as they are well built and readily available. The control temp or set point varies from 10 to 25 deg C and the coolant supply pressure is about 2 to 4 barg. I would appreciate if you could direct me to various models of TXV that can meet these requirements as most of the TXV seems to be for negative to less than 10 deg C set point. Thanks in advance.

    Best Regards,
    Benson



  2. #2
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,094
    Rep Power
    23

    Re: using a TXV as a control valve for cooling water or air

    Hi benson and welcome to our forum
    This is old school - pressure control. Just remember that you will need a difference of temp control related to pressure, Pressure - Temperature relationship. Cut in pressure is dependent on/if defrost needs and if the fan runs during the off cycle. Fridgies used this control on many cool rooms etc when I was an apprentice then the electronic controls came in and other stuff. So you will need to use a pressure controller to start and stop the compressor which will control the amount of cooling the TXV does or an EEV and a pressure temperature sensor. You could put your age - we would be more divulging in information as we could relate more and not just talk to a page or some blankness.
    Why not visit my website: www.rockncrystals.com.au ?

  3. #3
    Join Date
    Mar 2014
    Location
    Singapore
    Posts
    4
    Rep Power
    0

    Re: using a TXV as a control valve for cooling water or air

    Dear Tesla,
    need to add to my post that the cooling water or cooling air is that actual medium passing through the TXV.

  4. #4
    Join Date
    Mar 2014
    Location
    Singapore
    Posts
    4
    Rep Power
    0

    Re: using a TXV as a control valve for cooling water or air

    Sorry that I click the hide age too quickly. I am 50.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: using a TXV as a control valve for cooling water or air

    There is a lot of useful information on TXV on the Sporlan website.

    http://sporlanonline.com/literature-...nal-materials/
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: using a TXV as a control valve for cooling water or air

    A txv will not work in any sensible way if its regulating air or water directly, you would be better off looking at a solenoid valve controlled by a thermostat and possible a tap or similar restrictor you can use to balance they cooling load with the available duty provided by the cooling medium.
    Mostly found in Oxfordshire, UK :)

  7. #7
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,094
    Rep Power
    23

    Re: using a TXV as a control valve for cooling water or air

    MS is right TEV = no good for this app
    You could also use a two way water valve that uses a o to 10 volt dc signal. This is how it is done in many commercial buildings. You will also need a simple controller to generate the o to 10.
    Thinking about it there is a ready made self regulating plumbing valve tap controller used in showers - it may be a little higher range of temp than you are after but some are adjustable.
    Why not visit my website: www.rockncrystals.com.au ?

  8. #8
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    567
    Rep Power
    24

    Re: using a TXV as a control valve for cooling water or air

    Hi bensonThe valve Tesla is referring to is a tempering valve and I think they come in different ranges. There are many ways you can control the cooling depends how close to the set point you want to run. Any type of 3 way modulating valve would be suitable, these mix the warm return with the cold supply to achieve the desired temperature.Paul
    Born to fish, forced to work

  9. #9
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,645
    Rep Power
    23

    Re: using a TXV as a control valve for cooling water or air

    johnson controls V47 series valve, is a thermal statice water valve.

    http://www.johnsoncontrols.com/conte...valve/v43.html
    Now in Redvers Sask.

  10. #10
    Join Date
    Mar 2014
    Location
    Singapore
    Posts
    4
    Rep Power
    0

    Re: using a TXV as a control valve for cooling water or air

    Hi everyone,
    thank you very much for the information especially the Johnson control unit.
    I need something mechanical and I was hoping the HVAC TXV could do the job since they are so readily available.

    cheers Benson