    Choking in Refrigeration Plant



    Hi guys, we have been having a huge problem in our refrigeration plant.
    i am not the engineer so i don't know much about technically but i will writer as much as i know about the problem of this plant.
    We have a ***** gas based Refrigeration plant. Compressor pumps the ***** gas and gas runs through copper pipes from condenser then filter and then it goes to the tank which contains salt water and there are copper pipes inside it and gas runs within the copper pipes.
    Coming straight to the point.
    we are facing a huge problem right now the refrigeration plant it getting choked when it maintains the required temp and after that when we shut down the whole system for about 10 hours or more and restarts it then it works again, then after some time same problem happens again.
    Our engineer trying everything in order to fix it but couldn't fix it.
    he cleaned the whole plant many times with dry nitrogen gas using menthol liquid in copper pipes there is no leakage in the pipes and the pipes looks clean. there is little carbon which comes out within the copper pipes when we clean them using nitrogen gas. we changed the compressor, filter as well as expansion valve but the problem is still the same.
    Can anyone tell us what could be the problem?
    Is it happening because of the ***** gas or because of the pipes?
    Any help would be greatly appreciated.



  2. #2
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: Choking in Refrigeration Plant

    Maybe moisture in the refrigerant or worse a small water leak from your tank, you could get a refrigerant sample checked.

  3. #3
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Choking in Refrigeration Plant

    .

    Are you using the same refrigerant or did
    you replace the refrigerant for new each
    time you cleaned the system?

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  4. #4
    Join Date
    Mar 2014
    Location
    india
    Posts
    9
    Rep Power
    0

    Re: Choking in Refrigeration Plant

    Quote Originally Posted by Gibbo View Post
    Maybe moisture in the refrigerant or worse a small water leak from your tank, you could get a refrigerant sample checked.
    Thanks for reply i appreciate it. While cleaning up the system we can see few little drops of water coming out the refrigerant lines. What could be the reason? And for some times refrigeration system works for 3-4 days without any problem. I think it can't happen if there is water leakage in the tank? what do you think?

  5. #5
    Join Date
    Mar 2014
    Location
    india
    Posts
    9
    Rep Power
    0

    Re: Choking in Refrigeration Plant

    Quote Originally Posted by Rob White View Post
    .

    Are you using the same refrigerant or did
    you replace the refrigerant for new each
    time you cleaned the system?

    Rob

    .
    Thank you for the reply i appreciate it. We are using the same refrigerant after cleaning up the system. can you please tell me how we can find that there is moisture in the refrigerant and now it cannot be used in the system?

  6. #6
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,762
    Rep Power
    32

    Re: Choking in Refrigeration Plant

    Expansion valve will shut down with moisture in the system. Check compressor oil for colour change.
    Moisture in the refrigerant freezes at Expansion valve outlet when your plant is working.
    Install a LARGE capacity liquid line drier and a suction line drier while your at it.
    If there is a liquid solenoid valve for pump down, make sure your Low pressure switch is calibrated to turn off compressor above atmospheric pressure.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  7. #7
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,762
    Rep Power
    32

    Re: Choking in Refrigeration Plant

    It should have a HP/LP anyway. What type of gas are you using?
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  8. #8
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    439
    Rep Power
    31

    Re: Choking in Refrigeration Plant

    As the others say get a sample analysed of the refrigerant and get an oil analysis.
    You may have incorrect oil or contamination causing foaming or poor miscibility.
    I love the smell of Ammonia in the morning!

  9. #9
    Join Date
    Mar 2014
    Location
    india
    Posts
    9
    Rep Power
    0

    Re: Choking in Refrigeration Plant

    Quote Originally Posted by mikeref View Post
    Expansion valve will shut down with moisture in the system. Check compressor oil for colour change.
    Moisture in the refrigerant freezes at Expansion valve outlet when your plant is working.
    Install a LARGE capacity liquid line drier and a suction line drier while your at it.
    If there is a liquid solenoid valve for pump down, make sure your Low pressure switch is calibrated to turn off compressor above atmospheric pressure.
    Thanks for the reply.
    we are using liquid line drier. and in our refrigeration plant we are using R134a gas.
    Can you tell me is it necessary to use oil separator. and if there is moisture in the plant do we have to clean the oil separator as well?

  10. #10
    Join Date
    Mar 2014
    Location
    india
    Posts
    9
    Rep Power
    0

    Re: Choking in Refrigeration Plant

    Quote Originally Posted by hookster View Post
    As the others say get a sample analysed of the refrigerant and get an oil analysis.
    You may have incorrect oil or contamination causing foaming or poor miscibility.
    Thanks for the reply.
    The sample of the refrigerant is sent for the analysis. Now we are going to change the refrigerant as well as the refrigerant oil.

  11. #11
    Join Date
    Mar 2014
    Location
    india
    Posts
    9
    Rep Power
    0

    Re: Choking in Refrigeration Plant

    the Refrigeration Oil that we are using with R134a is ZEROL 200TD.

  12. #12
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    439
    Rep Power
    31

    Re: Choking in Refrigeration Plant

    With out looking at complete plant specification i.e compressors etc.
    The alkylbenzene oil would not be my first choice! I would go back to plant manufacturer to confirm why this choice of oil was made.

    I would probably have gone for a POE but as stated before a lot more detail on your plant would be required for an informed choice.
    I love the smell of Ammonia in the morning!

  13. #13
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Choking in Refrigeration Plant

    does his vac pump work correctly- fit a torr gauge at the furthest point of th vac pump- check for backdrops when vac pump isolated, maybe triple vac- increase surrounding air temp to improve vaccing process

  14. #14
    Join Date
    Mar 2014
    Location
    india
    Posts
    9
    Rep Power
    0

    Re: Choking in Refrigeration Plant

    But this ZEROL 200TD alkylbenzene oil is recommended by Plant Manufacturer. What do you suggest for R134a?

  15. #15
    Join Date
    Mar 2014
    Location
    india
    Posts
    9
    Rep Power
    0

    Re: Choking in Refrigeration Plant

    Quote Originally Posted by install monkey View Post
    does his vac pump work correctly- fit a torr gauge at the furthest point of th vac pump- check for backdrops when vac pump isolated, maybe triple vac- increase surrounding air temp to improve vaccing process
    Thanks for the suggestion we will try that?

  16. #16
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    567
    Rep Power
    24

    Re: Choking in Refrigeration Plant

    I agree with the other posters, I think you have to start afresh.
    Remove refrigerant, pressure test and repair any leaks, remove oil from compressor, flush system with a flushing agent, triple evacuation to 250 - 500 microns, new oil, new refrigerant.
    I tend to agree with Hookster about the oil, just remember POE oil is very hydroscopic.
    Paul
    Born to fish, forced to work

  17. #17
    Join Date
    Mar 2014
    Location
    india
    Posts
    9
    Rep Power
    0

    Re: Choking in Refrigeration Plant

    Quote Originally Posted by PaulZ View Post
    I agree with the other posters, I think you have to start afresh.
    Remove refrigerant, pressure test and repair any leaks, remove oil from compressor, flush system with a flushing agent, triple evacuation to 250 - 500 microns, new oil, new refrigerant.
    I tend to agree with Hookster about the oil, just remember POE oil is very hydroscopic.
    Paul
    Thanks for the suggestion. Now we are following this procedure. I hope everything will be fine now.

  18. #18
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Choking in Refrigeration Plant

    put your system minimum 24 h in vacuum to remove all moisture

  19. #19
    Join Date
    Feb 2014
    Location
    USA
    Age
    37
    Posts
    23
    Rep Power
    0

    Re: Choking in Refrigeration Plant

    Sounds like a busted tube. This is a brine chiller?
    R-134a is almost always POE. If you're having this kinda trouble you might need an eddy current test performed.

  20. #20
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    400
    Rep Power
    18

    Re: Choking in Refrigeration Plant

    suggest triple vacuum to drive out the last trace of moisture from system before re-commissioning.

  21. #21
    Join Date
    Feb 2014
    Location
    Canada
    Posts
    24
    Blog Entries
    1
    Rep Power
    0

    Re: Choking in Refrigeration Plant

    might be moisture of the refrigerant is not sufficient, change it and try

  22. #22
    Join Date
    Oct 2013
    Location
    England
    Age
    36
    Posts
    147
    Rep Power
    14

    Re: Choking in Refrigeration Plant

    Quote Originally Posted by airtrackinc View Post
    might be moisture of the refrigerant is not sufficient, change it and try
    Moisture of the refrigerant???? Hmmm

  23. #23
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    601
    Rep Power
    28

    Re: Choking in Refrigeration Plant

    Just make sure all solenoid valves are open while cleaning & vaccing the system! It's an easy thing to overlook.

  24. #24
    Join Date
    Oct 2008
    Location
    Ireland
    Age
    55
    Posts
    23
    Rep Power
    0

    Re: Choking in Refrigeration Plant

    From looking at the original post it suggests that the system stops working, then if it is stopped for 10 hours it starts working again. Is this without any intervention on the refrigerant circuit? If so I would suggest checking the Brine concentration. If the concentration is too low (or too high) this can cause partial freezing around the pipes causing low refrigerant pressure which could appear to be blocking of the expansion valve.