    Screw compressor



    Have got a York screw compressor it's a dxs36lasa46/50 problem I have got is when it gets up to full speed the compressor gives off a high scretching noise which is very loud haven't got much experience with York chillers would welcome some advice.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Screw compressor

    high screetchin noise when it stops- non return valve not seating- rotors run backwards as pressures equalize

  3. #3
    Join Date
    Feb 2014
    Location
    Liverpool
    Age
    46
    Posts
    24
    Rep Power
    0

    Re: Screw compressor

    The scretching is when the the compressor is running tho but when it starts up it is fine only starts this noise after a few hours if this helps

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Screw compressor

    obviously oil pressure is ok- prob worn bearing- check the running hrs and when it was last serviced

  5. #5
    Join Date
    Feb 2014
    Location
    USA
    Age
    37
    Posts
    23
    Rep Power
    0

    Re: Screw compressor

    You're not dumping liquid on it are you?

  6. #6
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Screw compressor

    Hi, Theboy


    Quote Originally Posted by Theboy View Post
    Have got a York screw compressor it's a dxs36lasa46/50 problem I have got is when it gets up to full speed the compressor gives off a high scretching noise which is very loud haven't got much experience with York chillers would welcome some advice.
    probably gets up to full capacity ....



    Quote Originally Posted by Theboy View Post
    The scretching is when the the compressor is running tho but when it starts up it is fine only starts this noise after a few hours if this helps
    so after few hours of running there is coming liquid refrigerant into suction like TF12 conclude in his post ...

    It is not easy to give some good suggestion,
    because we do not know anything about your plant ... try to give us more data ...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  7. #7
    Join Date
    Feb 2014
    Location
    USA
    Age
    37
    Posts
    23
    Rep Power
    0

    Re: Screw compressor

    For example:
    Refrigerant. Compressor application/Process application. Suction pressure and suction superheat. Discharge pressure and temperature. Slide valve position. Motor amperage. Refrigerant level in vessels ie receiver, accumulator/inter cooler/surge drum, expansion valve type....
    Screeching is not normal and if the compressor sounds like it is in distress, it probably is.
    In all seriousness I had a slide valve get out of calibration recently, the computer thought it was at 20% but it was really at 80% or more (im guessing) pulling 800 amps sounded terrible!
    Carry over
    The works
    Good luck!

  8. #8
    Join Date
    Feb 2014
    Location
    Liverpool
    Age
    46
    Posts
    24
    Rep Power
    0

    Re: Screw compressor

    Thanks for all the replys I checked the running pressures and they were all ok oil was also ok running amps were pulling about 49a on each phase have got a more experienced engineer coming to site now just trying to gain as much knowledge as I can for when we go back so I can check everything so thanks for all your suggestions.

  9. #9
    Join Date
    Jan 2011
    Location
    London
    Age
    38
    Posts
    43
    Rep Power
    0

    Re: Screw compressor

    The boy

    without the model of the chiller it's hard to assist you mate
    I suspect you are working on a York ycas if so then running at 49amps per phase you are not running at 100%fla I suspect the cause of the screeching is due to running at low load for long periods causing oil return problems for me to assist you further I need more details operating pressures,suction discharge and liquid temps,actual amps,entering and leaving water temp,oil delta p across oil filter ,oil pressure

  10. #10
    Join Date
    Mar 2014
    Location
    Bosnia i Hercegovina
    Age
    43
    Posts
    2
    Rep Power
    0

    Re: Screw compressor

    Dear friends, I have a problem with low outlet temperature of the liquid chillers York ynws.Alarm is "leaving chilled liquid-low temperatures." Setpoint is -6 C compressor and the temperature dropped to -7.6 C and stops working .. The temperature is then not lifted so that the compressor does not automatically move to work a long time.

  11. #11
    Join Date
    Feb 2014
    Location
    USA
    Age
    37
    Posts
    23
    Rep Power
    0

    Re: Screw compressor

    1st that should be an auto restart condition.
    It just means your machine is cooling the water too fast and it's dropping out and probably won't come back on for 20 minutes.
    Do you have a hot gas by pass? Is it working? If it is what are the parameters?
    Also you may want to look back in the engine room log to see when the slide valve and volume controls were last calibrated.
    Your screw may be out of calibration causing more capacity than what the computer is calling for.

  12. #12
    Join Date
    Mar 2014
    Location
    Bosnia i Hercegovina
    Age
    43
    Posts
    2
    Rep Power
    0

    Re: Screw compressor

    Chillers installed in 2005, and has only 6,000 jobs hours.Hot gas does not exist on the by-pass. Some servicer have done the first service and thereafter chillers is not working normally. Masters maintenance saying that chillers are 15 minutes, the set temperature, frees up to 15% capacity and then goes out and expel mistake leaving chiller liquid-low temperature.Chiller working on a system -10 c.