    Mar 2014
    India
    1
    Question difference between condenser pressure & condensing pressure
    Dear all,
    I am new in refrigeration. what is the difference between condenser pressure and condensing pressure.
    Condensing pressure means Compressor discharge pressure.
    I am using Ammonia compressor.Suction pressure indicates -13 Psig (minus 13) and Discharge pressure indicates 184 Psig.
    Any one tell the corresponding temperature.
    Shanbal.
    Apr 2008
    Canada
    253
    4
    Re: difference between condenser pressure & condensing pressure
    To answer your question you'll need to start by understanding compound gauges and pressure/temperature charts.
    Here is some light reading.
    1) Video - Understanding Compound Gauges & PT Charts
    The video is a little lame but informative.
    2) Using P-T Analysis As A Service Tool
    3) Ammonia PT Chart
    May 2012
    59
    1,528
    36
    Quote Originally Posted by shanbal View Post
    Dear all,
    Words that's all, words
    Condensing, condenser, discharge pressure , saturation, all words that
    describe a similar thing.
    Evaporating, evaporator, boiling, suction pressure, saturation all words that
    You need to understand the basics in refrigeration terms and definitions.
    The condenser is part of the system where the refrigerant condenses
    to a liquid at a certain temperature, that is the condensing or condenser
    pressure / temperature. That pressure can be read with a gauge that is fitted
    anywhere on the discharge side of the compressor all the way through to the
    liquid side of the condenser.
    Except for slight differences due to pressure drops (which we don't need to
    bother about at this level) the pressure / temperature reading will be the same
    at all points in that high side of the system and that pressure / temperature is
    only a reflection of what is happening in the condenser.
    Inside the condenser, the refrigerant is changing from a vapour to a liquid at the
    temperature / pressure shown on the high side gauge.
    Shanbal.
    Those numbers don't add up? Gauges read pressures and in refrigeration pressures
    indicate what the refrigerant is doing. In the high side the refrigerant is condensing in
    the condenser, in the low side the refrigerant is evaporating in the evaporator.
    It is all about temperature, but we can't do much with the temperature so we control
    the pressure and by controlling the pressure we can control the temperature.
    Rob
    Sep 2009
    Iran
    66
    672
    1
    condenser pressure is a your gauge pressure = ( your condensing pressure at ambient temperature + delta T )
    Apr 2001
    79
    5,071
    35
    Feb 2014
    37
    23
    Rob,
    I agree. If you're just starting out forget about pressures. Think temperature. Remember that all pressures have a corresponding temperature and in order for your condenser to reject heat to the atmosphere the condenser must be at a higher temperature than the ambient. In order to move heat energy out of your product or refrigerated space the evaporator TEMPERATURE must be lower than what your desired product temperature will be to absorb that heat energy.
    The greater the difference in temperature the faster the transfer of heat energy.
    This is the tip of a giant iceberg
    Great industry to be in
    Best of luck!!