    Oil in Liquid sight glass



    I am seeing a large amount of oil accumalate in the liquid sight glass on a system and a loss of oil in the compressor .
    But I thought the oil would sit in the evaporator during oil loss problems ?

    Any advice much appreciated

    Thanks



  2. #2
    Join Date
    Mar 2014
    Location
    croatia
    Age
    41
    Posts
    4
    Rep Power
    0

    Re: Oil in Liquid sight glass

    Could you describe the system? How many compressors, evaporators does it have a discharge oil separator, liquid reciver, suction separator... Tnx

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Oil in Liquid sight glass

    Short of refrigerant?

    Oil is normally carried around the system with the refrigerant but when there is a shortage of refrigerant the oil will accumulate wherever the refrigerant flow is low. (I assume the sight glass got a larger diameter than the liquid line?)


  4. #4
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,762
    Rep Power
    32

    Re: Oil in Liquid sight glass

    Liquid floodback. Cold compressor. oil foaming.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  5. #5
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: Oil in Liquid sight glass

    If it is a system that was retrofitted it could be the mineral oil that is floating around the system ,depending on the angle of the sight glass ie horizontal it can sit on the top of it for a while and would be very noticeable as it doesnt mix too well but will still travel around a ht system fairly easily.

  6. #6
    Join Date
    Jul 2002
    Location
    Derby
    Posts
    74
    Rep Power
    22

    Re: Oil in Liquid sight glass

    Fluid chiller , single recip comp , no liquid receiver , no oil sep , no accumulater , close coupled
    The sight glass is the very deep type, that always seems to have to fill up .

    Strange thing is that the sight glass will be full to start ( at higher water temp) then slow fill with oil and noticeable drop oil loss in comp , not much cooling happening , but superheat is Low , the after a while sight glass will start flashing (seem to partly empty) and no sign of oil, and oil level in comp will return.
    But I do think there maybe a little flooding back as oil temp does drop .

  7. #7
    Join Date
    Jul 2002
    Location
    Derby
    Posts
    74
    Rep Power
    22

    Re: Oil in Liquid sight glass

    It has been retrofitted in past to 407a , but has had numerous oil changes , I guess it could be some mineral oil , but still seem to be losing a large amount of oil from compressor

  8. #8
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Oil in Liquid sight glass

    From what you are describing the oil fluctuations/migration is a symptom and not a cause.

    Check your refrigerant level and meetering device(s).


  9. #9
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Oil in Liquid sight glass

    Got crankcase heaters?... pumpdown?... elevated evaporator?... overcharged?

  10. #10
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Oil in Liquid sight glass

    I had same problem 4 years ago and i find filter dryer is half blocked I changed that every thing went well.
    so check your filter .