    K plus vrv outdoor unit off



    Chaps

    we have inherited a building with a r407c kplus system which the sparks turned off the outdoor unit some 2 weeks ago (building being referb'ed) but not one controller threw up a U4 fault and continued to run.

    So how can a vrv lose the outdoor unit and not throw up a fault??



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: K plus vrv outdoor unit off

    Up in Kensington???

    Had the same thing occur on a site a few years ago, turned out the comms cable was "networked" between all the systems. As long as one outdoor unit had power all the indoor units were happy.


  3. #3
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: K plus vrv outdoor unit off

    closer to home in reading. They do have another (newer) system but I'm sure that isn't linked... The boss of the sparks thought it was 'spare' in the main distribution board so had it in mind to save a few quid on the job he was going to use that particular main breaker to power some new fuseboards going in..

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: K plus vrv outdoor unit off

    Been in Reading all day....glad to be home now.

  5. #5
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: K plus vrv outdoor unit off

    Quote Originally Posted by frank View Post
    Been in Reading all day....glad to be home now.

    well you should have phoned. Admittedly I was in Bristol all day but that's not the point

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •