    Blast Chiller high suction pressure



    Hi
    My friend went to replace evaporator coil on Williams Blast Chiller WBC20.He has changed coil and TEV both parts from williams and charged according to label 2kg of R404a .unit run down to -2 and cu out.He left site and 6 days later they rang saying it is not running.He went there today to find 200 psi high side and 100 psi suction pressure which was the case when he left it originally.Suction coming back cold and heat on the condenser but unit not running properly very slow like for a blast chiller. he carried out pump down test and said it is pulling to zero and then just below.Now he is booking compressor for replacement and i just wonder if it will sort problem or is there something else that need looking at ,completely lost on that one. when we phone williams they said it should be 1.4 kg as label is wrong lol so he decanet it today and put 1.2 still same pressures and results.
    Many thanks.



  2. #2
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Blast Chiller high suction pressure

    I would expect a recip (L'unite?) compressor to pull down and hold at least 15"hg, maybe even 20", so it does sound like bad valves etc.
    Mostly found in Oxfordshire, UK :)

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Blast Chiller high suction pressure

    had a recip on a freezer- only getting to -10 , suspected pot weak- pumped down only to 10 inch vac- replaced pot,-21 and capable of pulling a 17 inch vac as monkey says

  4. #4
    Join Date
    Oct 2010
    Location
    UK
    Age
    39
    Posts
    33
    Rep Power
    0

    Re: Blast Chiller high suction pressure

    brilliant lets hope that it will run ok when he goes change compressor.
    Thanks.

  5. #5
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Blast Chiller high suction pressure

    in all systems vacuum is very important especial in small systems .
    also in low temp it is better you put one extra low pressure control that control your solenoid valve ( if you have high pressure in suction pipe in starting time it close the solenoid valve until it comes down in large system) or you can use crankcase pressure regulator to protect your compressor and high pressure in condenser during stating time.