Thread: Fujitsu split fan motor
04-03-2014, 02:33 AM #1
Howdy - looking at a condenser - mod:AOT30LMADL.
Condenser fan not working - no power to the motor, do i just order up the circuit board or is there a common sensor fault not bringing it in like with some other models?
Pls let me know your ideas??
Thanx..
04-03-2014, 09:14 PM #2
Re: Fujitsu split fan motor
Probably the relay on the PCB. There are a couple of relays to control the fan. One to provide the power (K13) and another to switch between the speeds (K11). You can try giving the power supply relay K13 a little whack, might prove a point. Chances are the relay contacts have gone a bit pear shaped.
On the motor plug white is neutral, black is start winding which goes back into PCB to capacitor then to neutral, red and blue are the 2 speeds, guess you might have already figured that out though.
Thermistors shouldn't hold fan out, especially if you test in both modes. Always worth checking them though, got a sheet attached.
Cheers!Last edited by Tayters; 04-03-2014 at 09:28 PM. Reason: Ha, wrong attachment.
05-03-2014, 02:29 AM #3
Thanx mate - i'll check em out!