    Question Help with Mayekawa MYPRO CP IV Registers



    Hello everyone!

    I'm having a little issue with a screw compressor MYPRO CP IV. I've read the entire manual but I haven't found a register that allows to write via communication the desired Suction Pressure Setpoint. Does anybody who have worked with this compressor, if this is possible to do? If not, how can I give the compressor this setpoint?

    Thanks a lot for your help!

    Henry



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,355
    Rep Power
    39

    Re: Help with Mayekawa MYPRO CP IV Registers

    http://www.mayekawausa.com/techdata/index.html

    Henry,
    I have no experience with these but go to this link & at bottom is Mypro CPIV.
    on pages 38 to 41 is what I think you are looking for, CONTROL PRESSURE.

    Section 4.4 page 51,52 refer to remote capacity control.
    You would have to check if you have that option as well as relevant passwords if needed.

    If no luck suggest contact your nearest Mycom representative for guidance

    Hope this helps
    Last edited by RANGER1; 02-03-2014 at 07:20 AM.